Hello,
I just wired a 40 amp sub panel (rated for 125 amp) in my attached garage using 8-3 romex I had left over in my basement ceiling. The romex enters my garage to a box with cover plate where I connect to #8 thhn wires (using those huge blue wire nuts). The thhn wires run through 3/4" pvc conduit which runs straight up about 40" to the subpanel. At the moment I have nothing connected to the sub. I have two questions:
1. How close to the subpanel can I wire receptacles? The reason that I ask is that I would like to wire a 40 amp receptacle (50amp style) about 7 inches to the left. This will be used for a mig welder that require max 27amps, but has a 50amp plug. I would like to wire a 20-amp 120v GFCI receptacle to the right (also about 7 inches). Anything in the code that prohibits this distance?
2. The box with a cover plate I put in to connect romex to thhn is only about 12" from the floor. I've just read that receptacles need to be at least 18" from the floor in an attached garage. Does this height requirement also apply to a box with a cover plate?
Thank you very much for your responses and/or feedback!
I just wired a 40 amp sub panel (rated for 125 amp) in my attached garage using 8-3 romex I had left over in my basement ceiling. The romex enters my garage to a box with cover plate where I connect to #8 thhn wires (using those huge blue wire nuts). The thhn wires run through 3/4" pvc conduit which runs straight up about 40" to the subpanel. At the moment I have nothing connected to the sub. I have two questions:
1. How close to the subpanel can I wire receptacles? The reason that I ask is that I would like to wire a 40 amp receptacle (50amp style) about 7 inches to the left. This will be used for a mig welder that require max 27amps, but has a 50amp plug. I would like to wire a 20-amp 120v GFCI receptacle to the right (also about 7 inches). Anything in the code that prohibits this distance?
2. The box with a cover plate I put in to connect romex to thhn is only about 12" from the floor. I've just read that receptacles need to be at least 18" from the floor in an attached garage. Does this height requirement also apply to a box with a cover plate?
Thank you very much for your responses and/or feedback!