Minisplit capacity case study
The Metric System
I thought my experience regarding minisplit selection/sizing might be helpful to others.
As always, your application may vary and the best reference is a detailed manual calculation for your own specific space but I still think it's good to get a point of comparison from a real-world application.
Mountains of Western NC at about 2,100 ft. Geographically we're in the South but due to the altitude the climate is more midwestern. Think Cincinnati rather than Charlotte.
The space
A newly-built ~25'*55' stick-built garage that we added to our residence.
  • 2x 8'*20' insulated garage doors facing South
  • 1x man door to the outdoors
  • 1x man door to the living space
  • 4x 72"*80" sliding patio doors used primarily as windows
  • 1x ~3'*4' double-hung window
  • Vaulted ceilings, 16' at the peak
  • 2x ~2'*3' skylights on the South face
  • Concrete slab, insulated with 2" of expanded polystyrene board underneath and turned down at the edges
  • Provisions for radiant heat in the floor, not yet active
  • Ceiling R-38 fiberglass insulation
  • Walls R-19 fiberglass insulation
  • Between a common wall and a loft area there is a total of about 600 square feet of insulated walls separating the garage and the living space. These were previously exterior walls but became interior walls when the addition was put on. This is an important factor, as the other side of these walls can reasonably be expected to be ~65-75F rather than whatever temperature it is outside.
  • By code and by plan there is no air exchange between the living space and the garage beyond normal leakage and what we get from the man door opening.
The equipment
  • A no-name 24,000 BTU 21 SEER unit purchased from Costway in March of 2025 for $1,157 shipped.
  • Installed by me; I work in an adjacent industry and already had the necessary tools/skills to form the pipes and pull a vacuum etc. Nothing special about the install except that I ran the refrigerant and water lines inside of the wall before drywall went on. It was a bit of a hassle to package the 5/8" suction line within the wall but not too bad.
  • Indoor unit mounted on the center of a short-side wall about 8' off the ground.
  • Outdoor unit mounted on the ground directly below the indoor unit. It faces West and has no discrete protection from the elements, just the structure of the building next to it.
Results
Very good. We have had it in place through worst-case cold and hot days and it maintains the space at a comfortable temp even in these edge cases. As this is a working space we typically set the t-stat less aggressively than we do in the house.
  • In Winter it maintained the space at a setpoint of 65F even when outdoor temps were about 10F. In this condition an interior temp of ~68F was the limit of the system's capacity.
  • In Summer it maintains the space at a setpoint of 77F even when outdoor temps are about 95G with full sun on both the building and the outdoor unit. In this condition an interior temp of ~75F was the limit of the system's capacity.
  • Experimenting with capacity limits I've found that with exterior temps between ~15F and ~85F the system can hit any plausible indoor temperature I ask for, it only falls off under what are (for this area) extreme conditions that only occur a few days per year.
  • Dehumidification performance is excellent; humidity in the garage has stayed at about 50% throughout the Summer even as local RH is in the 80-90% range. There's a steady visible drip of water from the drain line, the grass in that area is growing faster as a result.
  • Temp recovery has not been an issue; after opening a big garage door for ~30 minutes during worst-case weather the space recovers in about 15 minutes once the door is closed. I attribute a lot of this to the thermal mass of the concrete slab, even in its current passive configuration it is a very effective regulator.
  • Even with the system blowing the length of the 55' room temperature distribution in the space is good, with (at most) 3 of variation across the length of the structure - about what you'd see from normal demand cycling. This is probably helped by the opposite end of the garage being tied into the house with a common wall, which reduces the thermal load on that side of the space and allows us to steal some heating/cooling from the living area.
Conclusions
I did the thermal calcs myself and knowingly undersized the system vs the standard recommendations that you'd get from a minisplit manufacturer's sizing tool. This smaller unit reduced cost, installation burden, and the level of required utilities and space and still gives very satisfactory performance in a working (rather than living) space. I would not have cut the capacity so close in a residence, but it is fine in a garage where temperature requirements are loose and you don't have the added heat load from cooking/showering/etc.
As a back-up, I originally had provisions for a second identical system to be installed if we found ourselves to be short on capacity and even routed the electricity and lines in-place to make future install easy. I think it is unlikely we will ever need to do that.
jack stand
Lakes Region Maine
Is it true that (beyond equipment capacity) that sizing is not nearly as important with these modulating? variable speed compressor as the older equipment with short cycling?
You sound like you know you chit for a truthful answer.
I've had several m/s systems installed and I was told this by the salesman about "sizing", but after living with them for 4-5 years now, I understand and agree. Those babies once to set temps just purr along slowly and quietly and the same for the outside unit.
Nice posting!
T
The Metric System
Yes, the risk of oversizing is greatly diminished with modern variable-capacity systems.
Modern minisplits have excellent turndown ratios (somewhere in the range of 4:1 to 10:1 depending on the equipment) and will happily run forever at just a fraction of their rated output rather than short cycling like ye olde single-capacity systems would.
It is much better to be a bit oversized than a bit undersized, as an oversized system will just ramp down a bit but an undersized system can't make up the capacity shortfall.
For somebody who can't/won't do the full calculation on what their space/application requires, the rule of thumb of "see what the manufacturer sizing tool recommends and then buy just one step bigger" is pretty reasonable.
jack stand
Lakes Region Maine
Thanks, while I got you on the "phone" 😉,
Am I correct that sizing was more important for ac (dehumidification) than in a heating mode?
I always try to learn or at least correct what I think I know.🫡
Mikes61
I’m another believer that going up one size is best, for a garage. The AC and heat demands are much greater in a garage than in a house. The house wont have a 16’ x 7’ door that opens several times a day. It also won’t have scorching hot car or two parked in it, ever.
I put a 3 ton, single head Mr Cool in my 1500ish sq.ft garage and it just spools down as it gets close to the desired temperature.
aggie113
San Antonio, TX
Firm believer in oversizing (with mini splits) for garages that will be used for working in. If you only calc based on space you end up with something that can maintain temp when not really in use. But open that garage door for a minute or two and bring a car in that's up to temp and you've gone beyond what that unit can handle. Having spare capacity means being able to quickly bring temp/humidity back to normal after that garage door is closed.
fitter30
Peace Valley,mo
I've got a 2- 24k 3head units. 5 - 9k wall and 1-9k duct. 1/4" and 3/8" lines For 1900 sqft house. Southern Missouri gets down to single temps. Can cool and heat with one unit till it get to extremes. Two systems were chosen for parts availability not to be left with nothing with a one system id one goes down. Also have 34k cast lp stove and 5k window unit for backup with 7k watt lp generator. Very rural.
pcmeiners
Have a Fujitsu low temp 12k for my garage, glad I did not go bigger. For a couple months that 12k heated my garage(1080sft) and ranch home ( 1250sft), same in the summer for a couple month( during the initial install phase of my (5) mini-splits . Also have a 9K for a bedroom now which does not have a lot of spare capacity. Capacity can vary even among the same series from a company. So it still a bit of a guessing game as to the capacity needed going by what the manufacturer's information states.
Both heating and AC capacity have to be carefully considered. Over-sizing or under-sizing by too much and noise by inside and outside units becomes a consideration . Undersized and the fans remain on high, much oversized and the units lowest fan speed can be noisy (both interior and exterior units), best off is a reasonable over size capacity.
American Locomotive
Rhode Island
Another thing to consider is that larger units are generally less efficient. All of the most efficient minisplits are smaller. Mitsubishi's most efficient unit at ~35 SEER2, is their 6,000 BTU Hyperheat unit. Every unit larger than that has lower efficiency.
Of course, once you get into the hyperheat/low-ambient class of minisplits, the word "capacity" really starts to become fuzzy. That "6,000 BTU" Mitsubishi has a nominal nameplate capacity of 6,000 BTU, but will actually max out at 14,000 BTU cooling and 20,000 BTU heating.
MushCreek
Upstate South Carolina
I did a full Manual J when I sized the equipment for our house. I had a 'professional' tell me that we need at least 2-1/2 tons. We use a single 12K mini most of the time, with a 9K in the master suite for extremes. In the shop, I went with a cheap 18K for my 900 square feet, and it works great for A/C. It's marginal for heat, probably because of the 12' ceiling and uninsulated 12 x 12 door, but it's adequate for my needs.
jjrbus
Florida
I have had "professionals" tell me so many things I learned to do my own AC and DIY installed minis in my house. Manual J showed about 27K btu, pros were insisting on 3 ton. At the Florida acadamy of air conditioning you can become a pro in 4 weeks.
I have 2 9k and 1 12K Daikins, the 12k does the bulk of the work so needs a deep cleaning more often.
MushCreek
The thing that's annoying about the guy who insisted I needed 2-1/2 tons is that he didn't even look at my house. If I had a 2-1/2 ton conventional system it wouldn't run enough to dehumidify. My house is ICF construction, R-50 in the attic, and I sealed every penetration everywhere. Even the orientation of the house on the land was considered in my design. We go for months at a time during spring and fall not using the HVAC at all.