What is a general range for delta T in a minisplit? I have a Mr. Cool and am wondering if it is up to par.
12,000 btu Mr Cool. Less than 500 sq feet, insulated, but not well.
Setting the unit at 68 or 70 degrees gives me 75 room temperature. That is fine, just surprised I can not get it lower. It is about 85 outside.
Intake at the blower is 76.6 (near the ceiling) and it blows out 48-50.
This is at 48% indoor humidity.
12,000 btu Mr Cool. Less than 500 sq feet, insulated, but not well.
Setting the unit at 68 or 70 degrees gives me 75 room temperature. That is fine, just surprised I can not get it lower. It is about 85 outside.
Intake at the blower is 76.6 (near the ceiling) and it blows out 48-50.
This is at 48% indoor humidity.
Matt and Poor Owner - thanks for the replies. This is getting interesting! I have been running and checking for a number of days. I have been running the fan on the highest setting. Yes, the house has low ceilings and a greenhouse attached that pumps some heat through the wall. The system has been in a few years - I think it did much better in the past. Wish I had taken some numbers in the past. It did get the room down to 68! But end of last summer the indoor unit froze up. It did have slow leak. I had it charged - the tech did not evac and weigh in the exact charge - just used gauges. He did not look for a leak because the quote for LOOKING FOR a leak was $800.00! ( paid less than $1000.00 for the system. He suggested I buy some gauges and refrig, let it leak, and recharge it once a year instead of paying his company $120.00 to do it. I decided it was a very slow leak at the Schroeder valve, bought the tool and replace the valve.
Curious as to how long it took to accumulate THAT much mold and how difficult was it to clean. Pictures? Is this a common problem with these systems, all mini's or just Mr Cools. Considering a couple for the BS&SG is my reason for askin
You *decided* it was a valve leak? I would love to decide where leaks are!
Find a reputable company who is not into ripping people off and have your system inspected.
Knowing the charge was guessed in and you now apparently have problems, I would have the charge recovered, any leak fixed, evac and weigh refrigerant back in according to factory charge. Then at least you know you have that part properly covered.