So, I have done two normal heat pumps but this is my first with flared connections. I have all the 410 tools and the flares are straightforward. However, I dont have a minisplit torque wrench but a normal torque wrench. I am using crows feet and the error for additional length (also tried at 90 deg which is not supposed to increase FTlbs even though it is a rotational rating and doesnt make sense that 90deg would change it) is well within the target torque range for the fittings. However, when I torqued down the 1/2inch copper it straight up torqued the flare off and never reached the click setting on the wrench. I then reflared the connecting and connected it. This time I torqued it and still didnt get a click. I stopped when I felt the connection getting a lot harder to tighten. I can pressure test at 350psi easy and if I get a leak just retighten. I use Co2 instead of nitrogen since I dont do this enough to justify buying the nitrogen tank, reg, and other parts. Co2 is cheap and I can refill the tank for $4 if this doesnt go well.
Anyone else experience the mfg torque ratings like this?
1/4 copper = 17.6-24.5 NM
3/8 copper = 33.3-41.2 NM
Anyone else experience the mfg torque ratings like this?
1/4 copper = 17.6-24.5 NM
3/8 copper = 33.3-41.2 NM