Started wiring a bathroom today. I have two 20 amps circuits using 12/2 Romex. One circuit for the heater and one for the lights and receptacles.
1. I am looking for a neater way of stapling multiple Romex lines to the stud. There are several places with two and three Romex lines running down the same stud.
I came across this online but I am open to suggestions...
2. How many runs of 12/2 Romex can I run through a 1" or 1.5" hole? I know that if they are run together for over 24", then they are considered bundled and may need to be derated. But they will simply run through a hole and then go on their merry separate way.
3. Does the six foot receptacle spacing apply in bathrooms as well? Between my last vanity receptacle and the bathtub is more than six feet. My toilet will be in that 6' space. I could easily add another receptacle but did not really want one near the tub or toilet.
4. I need to run Romex through the metal junction box on the bathroom fan/heater/light combo. I need a Romex clamp to insert in the junction box knockout. I am assuming that the clamp below is for conduit but I can not find one designed for Romex (or I don't know what I am looking for). Can anyone lead me in the right direction?
1. I am looking for a neater way of stapling multiple Romex lines to the stud. There are several places with two and three Romex lines running down the same stud.
I came across this online but I am open to suggestions...
2. How many runs of 12/2 Romex can I run through a 1" or 1.5" hole? I know that if they are run together for over 24", then they are considered bundled and may need to be derated. But they will simply run through a hole and then go on their merry separate way.
3. Does the six foot receptacle spacing apply in bathrooms as well? Between my last vanity receptacle and the bathtub is more than six feet. My toilet will be in that 6' space. I could easily add another receptacle but did not really want one near the tub or toilet.
4. I need to run Romex through the metal junction box on the bathroom fan/heater/light combo. I need a Romex clamp to insert in the junction box knockout. I am assuming that the clamp below is for conduit but I can not find one designed for Romex (or I don't know what I am looking for). Can anyone lead me in the right direction?