Modine Hot Dawg heater smell

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,889
Location
Fargo, ND
I still wonder about the painted flue pipe. It looks to be B-vent, but it can get very hot. Perhaps the heat is driving VOC's out of the paint. It might be as simple as replacing the vent pipe and don't paint it!

Was the vent pipe itself painted lately? Last few months?
 
To avoid these ads, REGISTER NOW!
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
I didn’t use the heater all weekend and Monday. I turned it on just now and first it just smelled like metal & warm dust for a few minutes and then I started to smell ozone, meter readings btwn .105-.163, then a minute later .195-.496. The air was thick & stuffy, I started coughing and I had to turn off the heater and open a window. After a minute or so of fresh air the readings went down to .045. Cleaning out the flu only helped a little bit at first and now we’re back right where we started.
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
I still wonder about the painted flue pipe. It looks to be B-vent, but it can get very hot. Perhaps the heat is driving VOC's out of the paint. It might be as simple as replacing the vent pipe and don't paint it!

Was the vent pipe itself painted lately? Last few months?
I will suggest that to my landlords. I’m not sure when it was painted
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
yeah, sounds like after it gets warm then it starts the problem. need to remove and replace all painted pipe
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Is this a legitimate, legal apartment or a warehouse convert?

Seems like a few potentially dangerous "features" of this space.
 

4x4Pete

Well-known member
Joined
Aug 26, 2019
Messages
792
Location
Stroud
I guess it's supposed to be o3.....but has anybody actually checked if the venting is properly sealed through the chase? The smell could be ozone and CO or any combination of products of combustion. The ozone seems unlikely so check for correct installation, especially proper venting. The company who checked it may or may not have checked thoroughly enough.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
I guess it's supposed to be o3.....but has anybody actually checked if the venting is properly sealed through the chase? The smell could be ozone and CO or any combination of products of combustion. The ozone seems unlikely so check for correct installation, especially proper venting. The company who checked it may or may not have checked thoroughly enough.
He has Ozone tests that show its ozone, lets not go away from the diagnosis and steer them in the wrong direction
 

4x4Pete

Well-known member
Joined
Aug 26, 2019
Messages
792
Location
Stroud
He shouldn't give up on the ozone, but he should at least check for CO. Ozone could be produced by the spark ignition but that would be minimal at most.
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
Test for CO! Could be venting is open in the chase.
Carbon monoxide has been tested for multiple times and is at 2 parts per million and I have smoke detector/carbon monoxide detectors in here carbon monoxide is not the issue
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
He shouldn't give up on the ozone, but he should at least check for CO. Ozone could be produced by the spark ignition but that would be minimal at most.
I have not seen any sparks from the fan at night time when I turned on the heat
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
Everybody I really appreciate all this feedback. Are there any professionals out there who could shine some light on why this could be happening? We’ve discussed the painted flue. I have not been using the heater because I don’t want to put my lungs in any more danger. I have three space heaters that I’ve been using every night, But the past times & EVERY TIME I turn on the Hot Dawg heater I smell chlorine and sometimes exhaust & natural gas…all I know is that an unauthorized build by a previous tenant for the enclosure happened and they also painted the flue and all the smells are coming out of the bedroom where the flue/ enclosure travel and they only happen when I turn on the heater and after the fan kicks on, these are the facts. I live in a warehouse converted into a live work apartment. LIVE means residential. The state of California requires all residential units to have a properly working heater & ventilation system. The heater has been inspected by a professional and everything seems to be in working order. I believe it is the painted flue & dusty enclosure that is a source of the problem. I bought an ozone detector with my own money I have been keeping a journal and tons of photographs and videos with dates and times and temperature/weather conditions like it’s my job. As of yet my landlords have not brought out a professional to test for ozone & measure air quality when the heater is turned on. Any professional help or Internet links or phone numbers that I can call to talk to professionals about this would be most appreciated thank you
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
I guess it's supposed to be o3.....but has anybody actually checked if the venting is properly sealed through the chase? The smell could be ozone and CO or any combination of products of combustion. The ozone seems unlikely so check for correct installation, especially proper venting. The company who checked it may or may not have checked thoroughly enough.
They checked the flue on the roof but I didn’t see it. They say it’s fine
 

Fly YX

Well-known member
Joined
Jul 31, 2017
Messages
1,422
Did anyone check to make sure the flu gases are going up the flu and not back into the living space. If that checks ok it’s probably the painted exhaust pipes or way they are ran.
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
Did anyone check to make sure the flu gases are going up the flu and not back into the living space. If that checks ok it’s probably the painted exhaust pipes or way they are ran.
Nope, no one checked for punctures or any leaks in the flue since it’s inside the enclosure.
 

Fly YX

Well-known member
Joined
Jul 31, 2017
Messages
1,422
Don’t know if it’s just the way the pic is but check this.
 

Attachments

  • 4981D33A-BFA1-4B44-902F-56F648F41496.png
    4981D33A-BFA1-4B44-902F-56F648F41496.png
    659.2 KB · Views: 52

Fly YX

Well-known member
Joined
Jul 31, 2017
Messages
1,422
And the back of the heater should be a blue flame across the burner. You could have a negative pressure in the vent going back into the living space.
 
To avoid these ads, REGISTER NOW!
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
Is that a close up of my flue from the pics I posted? Yeah I see what you’re getting at. It ONLY smells in the bedroom. Downstairs is normal. I really do think it’s the paint
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
New pictures of heater/flue/fan. I got a good deal on a used 10 ft ladder so I could see better. Haven’t turned on or touched this heater for a while because of health hazard.
 

Attachments

  • B4118578-FF0C-44C7-ADE7-ED5246BBF507.jpeg
    B4118578-FF0C-44C7-ADE7-ED5246BBF507.jpeg
    371.5 KB · Views: 40
  • D80383CD-4293-44CF-8761-7C201B0D64DB.jpeg
    D80383CD-4293-44CF-8761-7C201B0D64DB.jpeg
    245.9 KB · Views: 35
  • 05F1A61B-4E6F-4175-AF45-926D01C8C269.jpeg
    05F1A61B-4E6F-4175-AF45-926D01C8C269.jpeg
    292 KB · Views: 34
  • 10577C16-D270-47BE-BA85-F2D6D8DC8FA3.jpeg
    10577C16-D270-47BE-BA85-F2D6D8DC8FA3.jpeg
    270.7 KB · Views: 32
  • A3C8BE19-08AD-4576-ADC5-5B6B38AB25F1.jpeg
    A3C8BE19-08AD-4576-ADC5-5B6B38AB25F1.jpeg
    182.1 KB · Views: 33
  • 80204357-9176-4CBE-84DE-00296EFE4784.jpeg
    80204357-9176-4CBE-84DE-00296EFE4784.jpeg
    371.2 KB · Views: 37

Aileron

Well-known member
Joined
Apr 15, 2019
Messages
483
Location
outside
Is that space sealed up tight? It needs air to burn. It needs a combustion analysis done on it. Were did they test for CO. A proper combustion anaylsis is done in the flue piping exiting the heater. The outside of b vent should not be getting hot enough to burn the paint. That is why they use it.
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
Is that space sealed up tight? It needs air to burn. It needs a combustion analysis done on it. Were did they test for CO. A proper combustion anaylsis is done in the flue piping exiting the heater. The outside of b vent should not be getting hot enough to burn the paint. That is why they use it.
What space my apartment? Well there’s no weatherstripping around the front door and there’s definitely a breeze that comes in if that’s what you’re asking. I don’t know if they did a combustion analysis probably not but I’ll ask thank you for your reply
 

Aileron

Well-known member
Joined
Apr 15, 2019
Messages
483
Location
outside
No the space the heater is in. The fuel mixes with room air and the fuel burns depleting the oxygen in the room if it does not have any fresh air to make up and replace it. Usually 1 sq in for every 3ooo btu. If you put a screen over the fresh air opening it de rates the size of the opening by 25%. The flame will start going rich as you use up your air. You can produce co with too much air and not enough air. A combustion analyzer meter is the really only way to check.
 
OP
K

KVF

Active member
Joined
Apr 8, 2022
Messages
30
No the space the heater is in. The fuel mixes with room air and the fuel burns depleting the oxygen in the room if it does not have any fresh air to make up and replace it. Usually 1 sq in for every 3ooo btu. If you put a screen over the fresh air opening it de rates the size of the opening by 25%. The flame will start going rich as you use up your air. You can produce co with too much air and not enough air. A combustion analyzer meter is the really only way to check.
Carbon monoxide is not the issue that’s been checked several times and has not been detected at dangerous levels. The issue here is that the flu goes through the bedroom upstairs and every time the fan kicks on when I turn the heater on there is a strong smell of chlorine and ozone has been detected up to .4 to .6. With the windows open in the bedroom lower levels of ozone have been detected at .01 and slightly above. But it is counterproductive to open windows when you’re trying to keep the heat in. Heat just goes right out the window
 

Fly YX

Well-known member
Joined
Jul 31, 2017
Messages
1,422
I would have them replace the flu. With all the same size pipe. Wonder what the black stuff is ?
 

Aileron

Well-known member
Joined
Apr 15, 2019
Messages
483
Location
outside
JMO, there is no clean out on the flue piping, second, there is no drip leg in the gas supply line to the heater. Just two items that make me question its a DIY install and most likely a cut and run. That flue may not be maintaining a draft after the heater has been running for a while if it does at all. That fluehas to pull air from somewhere. If the heater can not draft correctly were is the byproducts going? Combustion produces NOX.


 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
JMO, there is no clean out on the flue piping, second, there is no drip leg in the gas supply line to the heater. Just two items that make me question its a DIY install and most likely a cut and run. That flue may not be maintaining a draft after the heater has been running for a while if it does at all. That fluehas to pull air from somewhere. If the heater can not draft correctly were is the byproducts going? Combustion produces NOX.


Since when does a gas flue require a clean out?
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
After all this confusion and lack of actual facts and data:
Maybe it’s not the heater ? Makeup air, sewer gas etc

  • Ozone can be confused by instrumentation with other oxidizing gases such as chlorine compounds, acid fumes, and oxides of nitrogen (NOx). Strong “reducing” gases, such as vapors of alcohol and solvents, can reduce the apparent concentration of ozone.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
JMO, there is no clean out on the flue piping, second, there is no drip leg in the gas supply line to the heater. Just two items that make me question its a DIY install and most likely a cut and run. That flue may not be maintaining a draft after the heater has been running for a while if it does at all. That fluehas to pull air from somewhere. If the heater can not draft correctly were is the byproducts going? Combustion produces NOX.

You may need to brush up on the Codes, This does not need a flue pipe clean out. and the drip leg is good to do, however would not effect what is going on.
 

Aileron

Well-known member
Joined
Apr 15, 2019
Messages
483
Location
outside
You may need to brush up on the Codes, This does not need a flue pipe clean out. and the drip leg is good to do, however would not effect what is going on.
It may not effect whats going on but its a hack install and wouldn't have passed here. Section 408.4 of the fuel gas code requires a trap in the gas line before that heater.
 
Joined
Mar 4, 2022
Messages
15
No sediment trap on the gas line, no condensate tee before the vertical section of vent. Shain't good!

@KVF, did you ever get this one figured out?
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
No sediment trap on the gas line, no condensate tee before the vertical section of vent. Shain't good!

@KVF, did you ever get this one figured out?
No tee is needed, and is not recommended on a b-vent system drip leg could be used. but i have never put one on for a garage heater.
 