I guess I haven't logged in for 7 years! I've got a 45HD that has been working well for 7 or so years. I turned it on a few weeks back because its getting cold here unfortunately. I go into the garage and I find the exhaust fan running but no heat. I get 3 flashes indicating a limit open. Testing doesn't show any issues although my testing might be flawed. I haven't tested the flame roll out switch yet. If I turn the power off for a minute and back on the unit will often fire up and run fine but next time there is a call for heat it won't run and the exhaust fun stays running. I have cleaned the flame sensor and check the pressure switch tube and exhaust ducting. Any ideas on what I can check next?
 
Last edited:
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,850
Location
Niagara Region, Ontario, Canada
read this on the web for 3 flashes
Limit switch is open
Limit Operation -
The limit switch is ignored unless a call for heat is pres
ent (W energized). If the limit switch is open and a call
for heat is present, the control de-energizes the gas valve
and runs the indoor blower motor on heat speed, and runs the
induced draft motor. The control will flash “3” on the LED until t
he limit switch closes. When the switch re-closes or the call
for
heat is lost, the control runs the induced draft motor through
post-purge and runs the indoor blower through the selected fan o
ff
delay. The control will return to normal operation after the blower off delay is completed.
 
OP
M

Matti

Well-known member
Joined
Nov 16, 2007
Messages
412
Location
Canada
I think that article is a solution to a different problem as the unit isn't starting and then shutting down early. I did do some more testing today. The unit wouldn't start and I have 3 flashing lights indicating open limits. There is 24 volts at the roll out switch and limit switches so the error doesn't make sense. Also the unit does run sometimes. I would like to test that there is actually 24 volts to the board but accessing the Molex plug with a multimeter is difficult. Assuming there is 24 volts then either the Molex plug is not making proper contact or the board is defective. The troubleshooting manual also says to check that the limit switches are not touching metal and shorting. Perhaps I could jumper the limit circuit to test this? I'm more of a mechanical guy than electrical.
 

eddieK

Well-known member
Joined
Mar 2, 2017
Messages
695
Location
Nampa Idaho
I think that article is a solution to a different problem as the unit isn't starting and then shutting down early. I did do some more testing today. The unit wouldn't start and I have 3 flashing lights indicating open limits. There is 24 volts at the roll out switch and limit switches so the error doesn't make sense. Also the unit does run sometimes. I would like to test that there is actually 24 volts to the board but accessing the Molex plug with a multimeter is difficult. Assuming there is 24 volts then either the Molex plug is not making proper contact or the board is defective. The troubleshooting manual also says to check that the limit switches are not touching metal and shorting. Perhaps I could jumper the limit circuit to test this? I'm more of a mechanical guy than electrical.

Check that the vent is clear, cap is intact etc
 
OP
M

Matti

Well-known member
Joined
Nov 16, 2007
Messages
412
Location
Canada
Yes I did check that first. This morning I checked the continuity in the limit circuit. Unplugged the Molex connector and checked it. Everything is fine - no open circuit (6 ohms). I have power through the pressure switch. This should mean the venting is ok. I'm out of ideas.:confused:
 
To avoid these ads, REGISTER NOW!
OP
M

Matti

Well-known member
Joined
Nov 16, 2007
Messages
412
Location
Canada
I ordered a new integrated circuit board. Apparently they sell quite a few.
 