I purchased a used Modine heater model HD45. It has been converted to LP. I want to run it off a small grill tank for now. When I open the tank valve, It seems to have too much pressure and I hear a hiss from the internal component the gas pipe screws into. Does this unit require a separate pressure regulator between the tank and the heater?? Thanks for any light you can shed on this.
 
To avoid these ads, REGISTER NOW!

4x4Pete

Well-known member
Joined
Aug 26, 2019
Messages
791
Location
Stroud
If you connected it without a regulator, the gas control valve in the unit is probably damaged. They are only allowed 1/2 psi. Anything more damages the diaphram. Usually inlet pressure is on the units rating label.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Agree with the comment about possibly ruining the gas valve when you connected it to tank pressure. A grill tank should be able to run a 45,000 btu heater. A 3 burner grill is probably about that much
 
To avoid these ads, REGISTER NOW!

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,836
Location
NW INDIANA
It will run it sure......but for how long?

Empty a tank every 15 hours doesn't sound too convenient
 
OP
N

njken

Member
Joined
Jan 19, 2017
Messages
7
I intend to get a larger tank. This is just to get me started. Thanks to all who replied.
 
OP
N

njken

Member
Joined
Jan 19, 2017
Messages
7
You guys were right. Gas control valve was toast. I replaced it and added the correct pressure regulator. Tested it on the bench and it fired up as it should. Too easy. I turned it over and mounted it to the ceiling. Hooked up the gas and power and tried to start. The exhaust fan comes on as it should but the flame never lights. There are 2 lights on the circuit board - green labeled OK and orange labeled flame. When the unit is plugged in but the thermostat is off the green light is lit. When thermostat calls for heat, The vent fan starts and the light is solid green. After a few seconds when it should fire, nothing happens and the green light starts to blink. The orange light never comes on. The only difference between the bench test and after mounting is that the unit was flipped 180 degrees. Any theories would be greatly appreciated. Thanks
 

Adk Mike

Well-known member
Joined
Jan 13, 2014
Messages
331
Location
upstate NY
I’ve had one the same model in my shop for 20 years.
The only service I ever did was replace the circuit board. About 75 bucks if I remember correctly.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,701
Location
Fargo, ND
You guys were right. Gas control valve was toast. I replaced it and added the correct pressure regulator. Tested it on the bench and it fired up as it should. Too easy. I turned it over and mounted it to the ceiling. Hooked up the gas and power and tried to start. The exhaust fan comes on as it should but the flame never lights. There are 2 lights on the circuit board - green labeled OK and orange labeled flame. When the unit is plugged in but the thermostat is off the green light is lit. When thermostat calls for heat, The vent fan starts and the light is solid green. After a few seconds when it should fire, nothing happens and the green light starts to blink. The orange light never comes on. The only difference between the bench test and after mounting is that the unit was flipped 180 degrees. Any theories would be greatly appreciated. Thanks
Plugged into the same power cord and outlet?

Controls on newer heaters and furnaces are polarity sensitive. They will do weird things if you mix up the hot and common, just like yours is doing.

Have you looked up the flash code for errors?
 
To avoid these ads, REGISTER NOW!