Modine propane heater question

tt455

Active member
Joined
Jul 27, 2011
Messages
35
Is the exhaust pipe to close to the sides of the roof? It is double wall but a couple of people brought it to my attention so I thought I'd ask here. If so, what can I do to correct the problem. If I try and widen the hole it may leak,I have it pretty well tared up. Thanks.

lewisgarage7006.jpg
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
B-vent requires 1" clearance to combustibles.

Sounds like you just ran the pipe though a hole and tarred it, proper way is to use a flashing made for that pipe size.
 
To avoid these ads, REGISTER NOW!
OP
T

tt455

Active member
Joined
Jul 27, 2011
Messages
35
B-vent requires 1" clearance to combustibles.

Sounds like you just ran the pipe though a hole and tarred it, proper way is to use a flashing made for that pipe size.

No,there is a flashing I installed for that size pipe. I guess I can cut some more for clearence.Thanks for the reply,
 