Hey guys,
Hoping someone has experienced a similar issue and can advise on "next steps".
I have a 2006 NY Thermal Trinity TI150 fully condensing, modulating wall boiler that provides heat to 3 zones. My garage floor, my breezeway, and the bonus room above the garage.
It is short cycling. What I see is when the boiler sees a heat call from any of the thermostats (wired into a taco 3 zone control box), pumps (zone and circulation) start up and the boiler goes into it's ignition cycle. It lights correctly and throttles up to maximum BTU. The water temperature through the boiler begins to rise. When the water temperature reaches the boiler set point, the boiler begins to throttle back the input BTU.
I can watch the gas valve setting as a 3 digit number on the display. It will begin to drop and when it gets down to about 60% (60% of 150,000 = 90.000 BTU)...the burner just cuts out. The boiler doesn't set any codes. It just immediately goes into a reignition sequence. It relights and throttles to full...but as the water temperature is still very near the set point, the 2nd time it will try to throttle down and cut out within about 30 seconds. At that point it's just relighting and shutting down maybe once a minute continuously.
So far I have cleaned the combustion chamber thoroughly and replaced the flame rod (flame sensor). Neither seemed to change the way the boiler acts at all.
Buddy at work says "Gas Valve" might be the issue. $400 is the best price I see on that....so not something I want to just try unless someone else has had this problem and that fixed it.
Honestly, I don't know if it's losing the flame sensor and that's causing the burner to shut down OR if the burner is shutting down on it's own....BUT I lean towards the first....because it seems to be burning, throttling down fine and then WHAM it just goes out completely. A few seconds later the boiler begins a purge cycle, and then an ignition cycle, relights....and repeat repeat repeat.
Any advice is much appreciated. I have called my HVAC guy this morning to get on his list, but at the time we put this in back in 2006 he had almost no experience with them. I've been maintaining it myself since then.
Hoping someone has experienced a similar issue and can advise on "next steps".
I have a 2006 NY Thermal Trinity TI150 fully condensing, modulating wall boiler that provides heat to 3 zones. My garage floor, my breezeway, and the bonus room above the garage.
It is short cycling. What I see is when the boiler sees a heat call from any of the thermostats (wired into a taco 3 zone control box), pumps (zone and circulation) start up and the boiler goes into it's ignition cycle. It lights correctly and throttles up to maximum BTU. The water temperature through the boiler begins to rise. When the water temperature reaches the boiler set point, the boiler begins to throttle back the input BTU.
I can watch the gas valve setting as a 3 digit number on the display. It will begin to drop and when it gets down to about 60% (60% of 150,000 = 90.000 BTU)...the burner just cuts out. The boiler doesn't set any codes. It just immediately goes into a reignition sequence. It relights and throttles to full...but as the water temperature is still very near the set point, the 2nd time it will try to throttle down and cut out within about 30 seconds. At that point it's just relighting and shutting down maybe once a minute continuously.
So far I have cleaned the combustion chamber thoroughly and replaced the flame rod (flame sensor). Neither seemed to change the way the boiler acts at all.
Buddy at work says "Gas Valve" might be the issue. $400 is the best price I see on that....so not something I want to just try unless someone else has had this problem and that fixed it.
Honestly, I don't know if it's losing the flame sensor and that's causing the burner to shut down OR if the burner is shutting down on it's own....BUT I lean towards the first....because it seems to be burning, throttling down fine and then WHAM it just goes out completely. A few seconds later the boiler begins a purge cycle, and then an ignition cycle, relights....and repeat repeat repeat.
Any advice is much appreciated. I have called my HVAC guy this morning to get on his list, but at the time we put this in back in 2006 he had almost no experience with them. I've been maintaining it myself since then.