Im going to make a single pole light switch into a hall or three pole switch, The new switch will be next to an existing light switch on a different circuit, in same box is it legal .or to code . I live in Wa.
The voltage limit rule for switches next to each other on different circuits:
NEC 404.8
(B) Voltage Between Adjacent Devices. A snap switch shall not be grouped or ganged in enclosures with other snap switches, receptacles, or similar devices, unless they are arranged so that the voltage between adjacent devices does not exceed 300 volts or unless they are installed in enclosures equipped with identified, securely installed barriers between adjacent devices.
You're good to go
or unless they are installed in enclosures equipped with identified, securely installed barriers between adjacent devices.
Where would you find a barrier for a 3 gang plastic box? I've got 3 home run light switches in a single box. Seeing this means I've got to fix it.
3 home runs - 1 each 120v going to 1 each 15 amp breaker. Yes, 360v in 1 3 gang plastic box. Therefore, where would I find barriers to securely install?
3 home runs - 1 each 120v going to 1 each 15 amp breaker. Yes, 360v in 1 3 gang plastic box. Therefore, where would I find barriers to securely install?
"Metering from hot to hot u will NOT have more than 120v difference between 2 ungrounded conductors." ("Hots")
I think Wylie meant to say 240 max, not 120 max.
Not being a jerk, Do not want to step on toes, but I am pretty sure it was a honest mistype.
Wylie - Please correct me if I'm wrong.
I'm pretty sure, metering from the one ungrounded to the other ungrounded, will give you either "0", or 240, depending on which Hot leg in the panel they are fed from.
Re the OP question - it's not rare to have ckts from separate breakers in j boxes, but usually see that in non residential work.
48 - Re: location of your new 3way sw - What do you mean specifically it will be "next to"?
How will you be adding a new switch "next" to an existing one.
It may matter, so tell please.
Marc
The NEC quote normally applies to 277 volt lighting circuits, when circuits on different phases are adjacent to each other, 480 volts is present which means more then 300 volts and the barrier requirement kicks in, since those voltages are not normally found in a residence ( I did come across residential 277V lighting once though) the barrier is not required since the maximum voltage present will be 240 volts. There is nothing to worry about, go for it.