Check you motor nameplate for the service factor (S.F.) Compressor motors usually have a 1.15 SF. 26A x 1.15SF = 29.9A If your running above the SF amperage the motor will be overheating.
Most manufacturers set up their compressors to run over the full load amps near the end of the pumping cycle, into the SF range. This is normally not a problem for cyclic loads where the motor has cooling time between cycles. If you run it hard and continuous (sandblasting) and it stays in the SF range the motor will die early from overheating.
Another thing to look at is the actual voltage while running, versus the nameplate voltage. The lowest running current will be had at the nameplate voltage. Above or below the nameplate voltage value the motor will pull more amperage for a given load. If your feeder or circuit is weak for the load or your utility voltage is high, this will exacerbate your problem.
Voltage can be modified with a buck boost transformer if necessary.
Reducing the size of the motor sheave is the most cost effective means for permanently bringing it down to the nameplate value. It will increase pumping time, but make the motor live longer, especially in hard use scenarios.
The other option is to reduce the pressure setting, lower head pressure equates to less motor load at the peak end of the cycle. The disadvantage here is more start stop cycles, which is hard on 1Φ motors with their capacitor start and centrifigual starting switches.