Does anyone know how to choose a start cap when the old one is missing and there is absolutely no data to be found anywhere?

Is there any formula based on motor amperage, etc?

This is for an old Milwaukee V-121 7" Bench Grinder with centrifical start switch that energizes a start cap circuit during start up. (cap is missing)

I did some experiments with a Turbo Cap:

At 5 MFD - Won't start
At 10 MFD - sluggish start
At 20 MFD - starts fine
At 25 MFD - starts strong

Should I just go with 25 MFD?? (at 330V rating)
 
Last edited:
To avoid these ads, REGISTER NOW!

KellyfromVA

Member
Joined
Aug 20, 2013
Messages
23
Location
Stafford, VA
I'd say that if you could fit a 25 MFD 330V cap onto the motor in a way that is safe, that should be fine. I assume this is a 120V motor? If so there is no harm in using a higher-rated voltage for the capacitor.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I just replaced a cap on an old 1/4hp 115V motor on a table saw and the cap it used was a 115V 138 MFD. I bought this one as a replacement..... http://www.galco.com/buy/NTE-Electronics/MSC125V124

I found this basic rule for MFD sizing....

This is not a FIX all, but a basic method for motor capacitors.

(2650 x Full load amps ) divided by supply Voltage = MFD

Example 2650 x 8amps = 21200 divided by 240volts = 88.33 MFD
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
D

Davefr

Well-known member
Joined
Jan 7, 2010
Messages
11,923
Location
OR
I just replaced a cap on an old 1/4hp 115V motor on a table saw and the cap it used was a 115V 138 MFD. I bought this one as a replacement..... http://www.galco.com/buy/NTE-Electronics/MSC125V124

I found this basic rule for MFD sizing....

This is not a FIX all, but a basic method for motor capacitors.

(2650 x Full load amps ) divided by supply Voltage = MFD

Example 2650 x 8amps = 21200 divided by 240volts = 88.33 MFD

Thanks! This is helpful. The nameplate says 6 amps and it's 120 VAC so that would imply 133 MFD.

It actually measures 3 amps under no load. Assuming no load at startup, (probably reasonable for a grinder), then that would imply 66 MFD.

Since it starts good at 25 MFD there must be lots of margin in start capacitor matching.

I think I'll try a bench test at close to 133 MFD and if it still starts strong I'll settle for that value.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
... there must be lots of margin in start capacitor matching.
...

The way they are made you will often fine a +100/-20% tolerance on values for electrolytic capacitors. So a capacitor that is rated as 50 microfarad may be between 40 and 100 microfarad.
 