I have a 240vac pump motor that currently has a starter attached. Long story short, the starter shorted out on the enclosure causing a smoke condition.
So two questions, can I hook the motor up directly, bypassing the starter, to see if the motor still works?
Second question, if the motor still works, can I simply install a 2 pole breaker in place of the starter?
Obviously
I don't understand the need for a starter
YOu could hook it up temporarily to see if it runs.
IF the motor doesnt have integral overload protection, then you need the starter.
IF it does, then you could omit the starter depending on what the motor is connected to.
You said its a hydraulic pump. What kind of equipment is it pumping hydraulic fluid for?
There may be a reason for the starter vs direct wired.
The data plate is really crusty, and old, and in a real inconvenient spot, but it looks like it is 1hp. The motor is for a hydraulic pump.
The unit is used for 2-3 hours once a year.
Does the HP rating matter on the starter, like putting your 5hp example starter on my 1hp (maybe) motor?
The current, melted unit specs to this one:
http://www.ebay.ca/itm/SQUARE-D-SIZ...AC-COIL-600-VAC-2-HP-1-8536SB01-/201102145126
yes it does matter.
You can use a higher HP rated starter on a lower HP rated motor as long as the overloads are set correctly.
You CANNOT use a lower rated HP starter on a higher HP rated motor.
Do you have a pic?
Not sure I understand your numbers.
Typically the higher voltage FLA will be half the lower voltage FLA.
So, if 19.6a is for 120v, then the 240v FLA would be 9.8a.