Motor starter for 5hp single phase

yelchevelle

Well-known member
Joined
Jun 15, 2018
Messages
178
Location
Hoover, AL
I have a Quincy 240 that I am putting a magnetic starter on. I have a NOS cutler hammer nema size 1. Says NO A10CG0. I am going to be honest in the fact that I have no idea how the mag starter actually works. This is a 3 phase starter, but I need to wire it up single phase 240 volts. I understand the principle, but not actually what’s going on. For the time being, I want my pressure switch to be wired into it, plus some kind of toggle switch to cut it off when I don’t want it live (so I don’t have to cut off the breaker. Long term, I want to also have the power cut off to it when I turn off the lights so that it only runs when I am in the shop(lights are on). I have seen other threads discussing what I want to do, but I don’t want to let the magic smoke out of any of my electrical components.
 

Attachments

  • 7619B78D-C883-4BA3-9AA0-EF9152119DDC.jpeg
    7619B78D-C883-4BA3-9AA0-EF9152119DDC.jpeg
    430.6 KB · Views: 35
  • C53E7BF6-9C6D-4D89-9AFF-B301E0576492.jpeg
    C53E7BF6-9C6D-4D89-9AFF-B301E0576492.jpeg
    368 KB · Views: 33
  • BAE16A85-3240-47F2-8DEE-55FA3E207319.jpeg
    BAE16A85-3240-47F2-8DEE-55FA3E207319.jpeg
    257.2 KB · Views: 30
  • A1AD8CFC-4EDB-4D7B-B7CD-3D3F71CDC1B2.jpeg
    A1AD8CFC-4EDB-4D7B-B7CD-3D3F71CDC1B2.jpeg
    278.4 KB · Views: 29
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,925
Location
Coronado, CA
I have a Quincy 240 that I am putting a magnetic starter on. I have a NOS cutler hammer nema size 1. Says NO A10CG0. I am going to be honest in the fact that I have no idea how the mag starter actually works. This is a 3 phase starter, but I need to wire it up single phase 240 volts. I understand the principle, but not actually what’s going on. For the time being, I want my pressure switch to be wired into it, plus some kind of toggle switch to cut it off when I don’t want it live (so I don’t have to cut off the breaker. Long term, I want to also have the power cut off to it when I turn off the lights so that it only runs when I am in the shop(lights are on). I have seen other threads discussing what I want to do, but I don’t want to let the magic smoke out of any of my electrical components.
I can come over and have a look at your problem. Are you within a reasonable distance to Coronado?
 
OP
Y

yelchevelle

Well-known member
Joined
Jun 15, 2018
Messages
178
Location
Hoover, AL
Sorry
I can come over and have a look at your problem. Are you within a reasonable distance to Coronado?

Sorry, unless you live on Coronado dr in Hoover, AL, you are a plane ride away. I got excited, because Coronado drive is really close to me, but I then looked at your profile and saw the CA followed your Coronado.☹️
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
A NEMA size 1 starter is too small for a 5 HP single phase motor, good for 3 HP though, while those Cutler-Hammer Citation starters are my favorite, they are obsolete & have been since around 1994-95. Your going to need a different starter.
 

CGT80

Well-known member
Joined
Aug 29, 2014
Messages
862
Location
IE, SoCal, USA
What is the amperage of your 5hp motor? They are not all the same. My 5hp baldor pulls as much as a new 7.5hp baldor.

I used a WEG 7.5hp single phase magnetic starter with a variable safety. It covers my 5hp motor and would allow me to upgrade to a new 7.5 if I decided to go bigger, but It may not work on a newer 5hp.

Amazon had many listed last year, but how it looks like Eaton is listed with no information on them and much higher prices, but the housing and internals look the same.

My motor is 28.5 amps with a 1.15 service factor. It can draw up to 32.77 amps and last I checked it was pulling around 27 amps when it shut off. A new motor is around 24 amps name plate.

The one problem I had with the adjustable is figuring out where to set it so it is low enough to protect my motor but not trip with high usage in the middle of a cnc plasma cutting session. I kind of guessed as I don't recall it tripping even on the lower settings. The markings are not that fine, so there is a little guessing.

I didn't want to break the bank on a starter and it seemed easier to use an adjustable unit.

Maybe someone has advice for properly setting that style. Is it super critical?
 
OP
Y

yelchevelle

Well-known member
Joined
Jun 15, 2018
Messages
178
Location
Hoover, AL
What is the amperage of your 5hp motor? They are not all the same. My 5hp baldor pulls as much as a new 7.5hp baldor.

I used a WEG 7.5hp single phase magnetic starter with a variable safety. It covers my 5hp motor and would allow me to upgrade to a new 7.5 if I decided to go bigger, but It may not work on a newer 5hp.

Amazon had many listed last year, but how it looks like Eaton is listed with no information on them and much higher prices, but the housing and internals look the same.

My motor is 28.5 amps with a 1.15 service factor. It can draw up to 32.77 amps and last I checked it was pulling around 27 amps when it shut off. A new motor is around 24 amps name plate.


Maybe someone has advice for properly setting that style. Is it super critical?

My name plate says it’s pulling 21 amps at 230 volts and 23 amps at 208 volts. My power runs a touch over 240. I thought going by the starters chart and the motor plate that 1044 on the low side were the correct size for the heaters. I have not checked the amps while running. My 3hp says 19 amps at 230 volts. Main reason I am wanting the starter is to keep from having all the power run through my switches. The Quincy has factory unloaders and the motor would probably be fine without a starter.

A NEMA size 1 starter is too small for a 5 HP single phase motor, good for 3 HP though, while those Cutler-Hammer Citation starters are my favorite, they are obsolete & have been since around 1994-95. Your going to need a different starter.

I am asking this because I don’t know, but is the chart and rating on the starter only for 3 phase, because my motor says it is pulling 21-23 amps, and the chart with the starter says it can go all the way up to 27 amps with the correct heaters

Edit: I guess the sfa are 25, so does that mean I need 1045 heaters?
 

Attachments

  • 2292ADB9-2083-4A23-92AB-25A2FF071957.jpeg
    2292ADB9-2083-4A23-92AB-25A2FF071957.jpeg
    393.5 KB · Views: 27
  • 6E3CEBE8-01E7-4C2C-9DAC-97048E72E6DD.jpeg
    6E3CEBE8-01E7-4C2C-9DAC-97048E72E6DD.jpeg
    309.1 KB · Views: 26
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
My name plate says it’s pulling 21 amps at 230 volts and 23 amps at 208 volts. My power runs a touch over 240. I thought going by the starters chart and the motor plate that 1044 on the low side were the correct size for the heaters. I have not checked the amps while running. My 3hp says 19 amps at 230 volts. Main reason I am wanting the starter is to keep from having all the power run through my switches. The Quincy has factory unloaders and the motor would probably be fine without a starter.



I am asking this because I don’t know, but is the chart and rating on the starter only for 3 phase, because my motor says it is pulling 21-23 amps, and the chart with the starter says it can go all the way up to 27 amps with the correct heaters

Edit: I guess the sfa are 25, so does that mean I need 1045 heaters?
A size 1 starter is 3 HP single phase at 240V, MAXIMUM the amperes do not matter.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,966
Location
Peace Valley,mo
Just power L1 and L2 leave L3 empty. It will still the overload heater installed to work. Heaters need to resized just purchase 2 #1044 L3 doesn't care about the size since it's not protecting anything. If you can used ones don't be afraid to buy them. That starter is old school and very well made compared to what is out there now
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Just power L1 and L2 leave L3 empty. It will still the overload heater installed to work. Heaters need to resized just purchase 2 #1044 L3 doesn't care about the size since it's not protecting anything. If you can used ones don't be afraid to buy them. That starter is old school and very well made compared to what is out there now
So a undersized starter is OK?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Just power L1 and L2 leave L3 empty. It will still the overload heater installed to work. Heaters need to resized just purchase 2 #1044 L3 doesn't care about the size since it's not protecting anything. If you can used ones don't be afraid to buy them. That starter is old school and very well made compared to what is out there now
Bad advice

And if it has phase loss protection then it wont work when leaving one terminal unused...
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,966
Location
Peace Valley,mo
Bad advice

And if it has phase loss protection then it wont work when leaving one terminal unused...
Doesn't have phase loss just amperage. Wouldn't doubt that starter is 20 years old or more. What is so great about these starters coils, contacts, aux switches and overloads are changeable. Aux switch has n.o. contacts need n.c. Take it apart flip a contact.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Doesn't have phase loss just amperage. Wouldn't doubt that starter is 20 years old or more. What is so great about these starters coils, the contacts, aux switches and overloads are changeable. Aux switch has n.o. contacts need n.c. Take it apart flip a contact.
Try more, it was discontinued after Eaton bought the distribution & controls div of Westinghouse in the mid 1990's, Not sure if Eaton still supports the Citation starters. The minimum is NEMA size 1 1/2 for 5 HP 1Ø motors.
 