have a detached garage, approx 700' square and 70' from main house. original sub panel in garage is decent (100A main lug, lots of room for breakers maybe 24?) but the feed from main panel to sub panel was horribly wrong (10/3 UF buried 12" under grass). voltage swing leg to leg was 85V/150V when starting larger tools - unusable setup.
i ripped all that out and ran 75' of conduit 27" deep, pulled (3) #4 and (1) #6 THHN from house (SER from main panel to house exit). voltage is quite nice (swing is around 0.1V now). main panel has 60A breaker feeding subpanel.
one of my more bewildering issues (for me) is this: i moved the sub panel in the garage to a different wall to create a straight shot conduit run - if i had ran conduit to where the panel was originally it would have taken 350' instead of 250' (big house) and i would have killed 12 trees digging the trench. a straight shot killed no trees and knocked off 100' however the ufer ground hookup is still where it always was. right now i have no garage building ground (i do have ground run to main panel) and i dont know if its better to run a new ground where the panel entrance is now or run a #6 50' through the wall and somehow legally tap the ufer to the panel.
i'm out in the boonies. my electrician said dont hook up a building ground out here but i lay awake at night worrying. the advice (unofficial) i have gotten locally is to run two 8' rods 6' apart where the panel is now and dont use the existing ground but i tell you what - the ground is intolerable to get through. its like cement; the trench digger struggled and gasped going through this stuff, and there are large rocks down there. i am not seeing two ground rods going much past 12" before massive issues crop up.
can i hook up the original ground by running #6 50' through the walls? i know NEC wants a contiguous run but allows certain connections.
i ripped all that out and ran 75' of conduit 27" deep, pulled (3) #4 and (1) #6 THHN from house (SER from main panel to house exit). voltage is quite nice (swing is around 0.1V now). main panel has 60A breaker feeding subpanel.
one of my more bewildering issues (for me) is this: i moved the sub panel in the garage to a different wall to create a straight shot conduit run - if i had ran conduit to where the panel was originally it would have taken 350' instead of 250' (big house) and i would have killed 12 trees digging the trench. a straight shot killed no trees and knocked off 100' however the ufer ground hookup is still where it always was. right now i have no garage building ground (i do have ground run to main panel) and i dont know if its better to run a new ground where the panel entrance is now or run a #6 50' through the wall and somehow legally tap the ufer to the panel.
i'm out in the boonies. my electrician said dont hook up a building ground out here but i lay awake at night worrying. the advice (unofficial) i have gotten locally is to run two 8' rods 6' apart where the panel is now and dont use the existing ground but i tell you what - the ground is intolerable to get through. its like cement; the trench digger struggled and gasped going through this stuff, and there are large rocks down there. i am not seeing two ground rods going much past 12" before massive issues crop up.
can i hook up the original ground by running #6 50' through the walls? i know NEC wants a contiguous run but allows certain connections.