So just the worm clamp? First time using this type of appliance adapter. Other types with the screw holes are sold out locally. Thanks in advance!that looks like a Saf-T Vent Category III . and if it is here is the exact quote from the manufacture
- Engineered with laser welded seams for leak-proof installations and a factory-applied silicone gasket (no RTV sealant required) makes for an easy installation
this might be easier https://heatfab.com/uploads/EZ_Seal_Catalog.pdfSo just the worm clamp? First time using this type of appliance adapter. Other types with the screw holes are sold out locally. Thanks in advance!
Installing the venting for my 125KBTU unit and just made the decision to switch to vertical instead of horizontal. With vertical am I able to use B-Vent instead of Category III?
Thank you!!Vertical allows for B vent provided your horizontal run is 75 percent or less than the vertical portion. So if you have 10 feet of vertical rise, and your horizontal is less than 7.5 feet, you can use B vent.



Single wall clearance to combustibles is generally 6 inches. Clearance to combustibles can be reduced with proper barrier materials but I think you'll have to blast a new hole to make it right. Thimble appears to be the wrong type, doesn't have proper clearance around the circumference.Thanks for the response.
I might have screwed up royally then...definitely admit I got over my head.
I do think you're right it's a B vent thimble. I had the guy at Menards help me find parts and because they didn't have the kit, he was reading parts of the kit and was handing me individual parts...guess he might've read the wrong part number.
The single wall part is definitely my fault for not knowing there's category III single wall. Also that hole was cut too close to the soffit so hard to get it away from it now. It's about a couple of inches away. The manual didn't have any specs over how far away from soffits.
Any tips on salvaging this?
I want to try to avoid another hole but if I have to then I have to. My biggest worry is how close the vent is from the soffit and if any rain water will enter the T with it not being covered under the soffit.
I can definitely purchase the dualwall cat III parts and make it cat III all the way.
The B vent thimble does have clearance as the portion inside the wall is 2" wider than the vent but yes I need to just go get the right thimble.
Thanks guys!
I’m gonna run single wall cat III from the heater to the thimble then double wall to the termination. Looks like how far the termination extends past the soffit won’t be a problem then. I’ll switch out the thimble and replace the galvanized parts and then I think I’ll be goodI can confirm that the single wall cat III gets stinking HOT during operation. I touched it like a certified ******* after kicking it on the first time. You're going to at least discolor that soffit. And the termination should not end under the soffit either. Do yourself a favor and re-read the installation instructions if you aren't sure, they pretty clearly spell out the required clearances.