Mr Heater Big Max 80K BTU Allowable Horizontal Termination Caps

Skip707

Member
Joined
Jan 3, 2018
Messages
13
Hello. I just purchased a Mr Heater Big Max 80K BTU Garage Heater and will be using Propane. My question is what type of termination cap is allowed for the CAT3 type venting. The manual only shows a T Pipe that is open on both ends. Are there other type termination caps I can use that are safe? My concern is with just an open pipe will air just be coming into the garage when the unit is not running and alot of hot air coming in during the summer? Is there a different type of termination cap that I can use that has a flap or something to keep air from coming back in garage or water running back towards unit when its raining since pipe slopes down into garage. Any help and pics would be greatly appreciated. Thanks
 
To avoid these ads, REGISTER NOW!

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
You want a cat III termination cap for Horizontal vent. Google it for choices. Duravent is a popular choice.

You should be following fig. 6 in the manual (link attached) for Horizontal Residential venting (assuming your not a commercial buisness or zoned as such). Regardless, you could check with your state and local codes first as they take jurisdiction over anything else (that is if you have any plans to do it by code).

Although my heater/Install is a bit older and the cat III requirement doesn't apply, the dimensions and look are the same.

https://www.northerntool.com/images/downloads/manuals/27456.pdf
 

Attachments

  • IMG_0129A.jpg
    IMG_0129A.jpg
    147.3 KB · Views: 110
Last edited:

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Open vent is an open vent..........the cap makes very little difference in the back flow.
 

metschers

Well-known member
Joined
Dec 17, 2010
Messages
136
Location
Billings, Missouri
Skip
I had the same problem. After several hours of research, I went with a kit from gadgetsgo.com. It included the everything needed, including a backdraft flap. Plus it was an all stainless steel kit(flex vent)Ordered, 2 day delivery.
Saved me a lot of $$$$$$.

Hope that helps you out,
SM
 

Attachments

  • 2017-10-31 10.41.42.jpg
    2017-10-31 10.41.42.jpg
    121.7 KB · Views: 102
  • 2017-10-31 10.45.40.jpg
    2017-10-31 10.45.40.jpg
    135 KB · Views: 111

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
Skip

I had the same problem. After several hours of research, I went with a kit from gadgetsgo.com. It included the everything needed, including a backdraft flap. Plus it was an all stainless steel kit(flex vent)Ordered, 2 day delivery.

Saved me a lot of $$$$$$.



Hope that helps you out,

SM



MUST
KNOW
MORE!

I really like the look of that boot!
Tell me more, link to your specific kit, please.


Sent from my iPhone using Tapatalk
 

metschers

Well-known member
Joined
Dec 17, 2010
Messages
136
Location
Billings, Missouri
MrSurly,
Here's the link...https://gadgetsgo.com/2ZVWB04-Wall-Hung-4-inch-Vent-Kit-Stainless-Steel-Tankless.html
Actually it's still on sale for $169.88 free shipping ( I opted for 2-day express delivery 5.00).
The boot/wall thimble is flat, so I used a couple of 1x1 clamped in a vice and made my bents to match the contour of the corrugated steel siding on the outside. On the inside, I left the thimble flat and built a spacer out of 2x6 to protect the insulation. The wall thimble is 2 pieces that are telescopic so they fit together very tightly. Surrounded by the 2x6 "box", it forms a double walled transition thru the wall. Once together the outside dryer vent looking piece slides on and clamps. The 4"dia kit(Z-vent) is all stainless with internal gaskets on each piece. I used a little lithium grease on the gaskets for easier assembly figured it would burn off. Also wear gloves, the pieces are very sharp. The kit included a 90 degree elbow, but I needed a 45. I called and talk to Ross, he said no problem and switched the 90 for a 45. I'm not sure if my assembly is to "code", but it works very well.
If you have any questions, contact Ross at that link. Super nice guy.

Hope that helps
Regards,
Steve
 

Attachments

  • 2018-01-06 19.45.48.jpg
    2018-01-06 19.45.48.jpg
    19.1 KB · Views: 57
  • 2018-01-06 19.44.58.jpg
    2018-01-06 19.44.58.jpg
    31.8 KB · Views: 42
To avoid these ads, REGISTER NOW!

metschers

Well-known member
Joined
Dec 17, 2010
Messages
136
Location
Billings, Missouri
Bobbyjean,
So far so good, I've not had any problems. I pitched the vent down slightly towards the outside and haven't had any condensation issues. I installed the heater in early November 2017. The temperature here, like the rest of the country has been from one extreme to the other. It was -2 the other night and has been in the teens thru out the week. This week is suppose to be 40-60 degrees.
The damper is actually installed right off the heater outlet so it won't freeze up.
I only use the heater when I'm working in the shop. I monitor the temperature and its never dropped below 25 dgrees (3" insulation on walls/ ceiling).
The other day it was 14 degrees outside, being a 100K heater it took about hour to bring the inside temp to 65 degrees.

Regards
 

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
Thanks for the info, I have now ordered this set up with the 45 after speaking with Ross.
The issue tyhat I don't know the answer to right now is whether the "universal" adapter will fit to the Mr.Heater (this unit has a really *short* transition) and I'm keeping my fingers crossed.
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
Do the tankless water heater horizontal vents meet CAT3? I noticed they are about half the cost.
 

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
Do the tankless water heater horizontal vents meet CAT3? I noticed they are about half the cost.

It 'says so'


*edit* I've not found anything that indicates a difference for water heater/furnace/space heater/boiler/spa/pool heater, whatever. Just "Fuel gas vent" class X
 

Attachments

  • Zvent UAA2.jpg
    Zvent UAA2.jpg
    67.8 KB · Views: 38
Last edited:

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Do the tankless water heater horizontal vents meet CAT3? I noticed they are about half the cost.


My heater instructions specifically called for TEE vent.

The standard cat III tee is $50 at Menards.

9490TEE_173681_front.jpg
 
Last edited:

MrSurly

Well-known member
Joined
Jan 15, 2014
Messages
1,671
Location
East Texas
I can’t seem to find my instruction book today(!)
I do recall the drawings both showed tee style.
I don’t recall the text saying ‘must be tee’ but I don’t actually doubt it.
I had mentioned my plan to one of the city inspectors and he said they don’t have a requirement but just mfrs requirement and if I had a vent rated class iii then he was happy. But I’ll have to investigate the book again.
Also, I wonder why the tee?


Sent from my iPhone using Tapatalk
 
Last edited:

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Depending on where you're located you may need to use a high wind termination cap, especially if you are taking combustion air from inside.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
The other call out in the instructions:

“Do not damper or add heat recovery devices to the flue piping. Failure to open such a damper prior to operating the gas unit heater will result in the spillage of flue gas into the occupied space.”
 