Mr Heater install

tc_rain

Member
Joined
Dec 12, 2013
Messages
6
I am installing a Mr. Heater MHU 50. I have the gas and thermostat ran. I am now about to run the electrical to a dedicated circuit using 14/2 wire to a 15 amp breaker. The run is no more than 12’. Anyone see a problem with what I have so far? This is my first time at doing something like this so any help or criticism is appreciated.
 

Attachments

  • photo.JPG
    photo.JPG
    97.2 KB · Views: 216
To avoid these ads, REGISTER NOW!

cdsvt

Well-known member
Joined
Jul 25, 2013
Messages
52
I don't use anything less that 12/2 anymore, but if that meets the requirements, then it seems fine.

Looks like you are missing a vent pipe... :)
 
OP
T

tc_rain

Member
Joined
Dec 12, 2013
Messages
6
Vent pipe is next after electrical. I think I am going to move up to 12/2 too.
 

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
Obviously the vent and It looks like you may have a service swich on the rear of the unit. If not I would replace the plug and outlet combo with a service switch box. Remove the outlet and add a 2" extension box, Install a switch, cut the plug off the cord and wire into the box.
If you do have the switch, just delete the plug/outlet combo.

Whats your vent and tank plans/setup ?
 

Attachments

  • DSC01781.jpg
    DSC01781.jpg
    136.4 KB · Views: 165

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
14-2 is more then enough, I would be shocked if the max amps on that unit is over 5.

Cord and plug are fine, I prefer to hardwire and mount a switch on the unit but cord and plug will serve just fine.
 
To avoid these ads, REGISTER NOW!
OP
T

tc_rain

Member
Joined
Dec 12, 2013
Messages
6
Thanks for all the help. The vent goes up last since I am going to have a professional come out and cut a hole in my roof. I just can’t bring myself to do it. I am sure I could but just too apprehensive it might leak sometime in the future. I will also have him look over the rest of the install to make sure everything is okay and won’t burn down or blow-up my house later since it is attached.

The little box in back where the power supply connects is not a service switch; it is just an electrical box to make the electrical connection. I just started running the wiring and went with 12/2 since I had about 50’ on hand. As I started to connect it, I noticed a tag inside the heater that states it only draws 3 amps max (see about the middle of the attached picture). Since I only know enough about electricity to be dangerous, why does this need to be on a dedicated circuit? I believe my coffee maker draws up to 8 amps. Also, why would it need a service switch if it could just be unplugged?

Again, thanks to everyone for the help. I do not doubt what everyone stated, I am just trying to learn and reason this myself.
 

Attachments

  • photo (1).JPG
    photo (1).JPG
    133.3 KB · Views: 42

dipper

Well-known member
Joined
Jun 27, 2007
Messages
759
Location
Rochester, NY
I think you are fine on a 15A circuit, as noted it only draws 3amps, so no real benefit to bump to the larger 12/2 cable. I think it's a cleaner install to have it on a separate circuit, makes it easy to troubleshoot if you have too. I put mine on a dedicated circuit but it is also shared with the OHD opener which i have yet to purchase and install.

I think either the cord plug or a switch at the unit is a good means of disconnect.
 

Woodchopper46

New member
Joined
Dec 9, 2013
Messages
3
Location
Ontario, Canada
Since I only know enough about electricity to be dangerous, why does this need to be on a dedicated circuit? I believe my coffee maker draws up to 8 amps. Also, why would it need a service switch if it could just be unplugged? [UNQUOTE]

A dedicated circuit = less chance of heater being turned off by mistake,
also no worry about something on the same circuit burning out & throwing the breaker, then you have a cold garage.
As far as service switch or plug, either will work. Some municipal codes require a switched service for various reasons. I prefer switched, IMO it is just handier.
 

kenfath

Well-known member
Joined
Oct 17, 2006
Messages
358
Location
Upland, CA
'I think' the reason for having a dedicated circuit is the heater is considered a furnace; and furnaces are required to have a dedicated circuit.

The hard wiring vs. a plug seems to be a regional thing. When I was in the midwest and east, only found hard wired installations with a nearby switch. In S. California and Arizona I've only found plug ins. I've had both installations and finally decided I have no preference. Both work equally and serve the same purpose.
 