This is a cross post form General Garage Discussion / Wire Placement thread.

MRB, you make note that there is No grounding electrode in the building
ok, so you do have 4 wires with isolated neutral and ground, but the romex is a problem as is the lack of grounding electrodes
It's interesting you bring this up, i was reading a couple of weeks ago here
http://forums.mikeholt.com/showthread.php/132692-Multiple-Earth-Grounds

And the way i saw it, external buildings don't get a ground rod (egc).

Am I reading the post wrong or missing something?

Please educate me (seriously, I am not trying to be a smart ***, just trying to learn).

Thanks
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
EGC is not a ground rod. a ground rod is a grounding electrode. GEC is grounding electrode conductor -the wire coming from the ground rod. The EGC is equipment grounding conductor which is the ground wire from the subpanel back to the panel serving it.

read this in its entirety and ignore the section on ungrounded systems in industrial facilities http://ecmweb.com/grounding/electric_grounding_vs_bonding_2/#
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
also note that its not 'multiple grounds' each of these things serves a very different function. its not an issue of one is good so two must be better.
 