I have (4) 3-phase 208 1/2 hp. fan motors with a FLC of 2.4 amps each that I would like to wire to one branch circuit. Each will have its own starter and disconnect. They will all come on together and go off together by a remote location switch. When sizing the OCPD for this branch circuit, am I'm reading 430.53(A) correctly where it says 15 amps max. If this is correct, I'm thinking it may trip the breaker on start up.
 
To avoid these ads, REGISTER NOW!

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I read that to say max 20 amps for less than 1 HP motors, but there are other requirements too.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,889
Location
oregon
Have you considered time delay relays in the start circuit so that you can cascade the start of the fans by a given time delay on three of them?

lg
no neat sig line
 
To avoid these ads, REGISTER NOW!

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,984
Location
Rhode Island
I think you would probably be okay. It's only 2HP total worth of motors. Most breakers won't insta-trip until they hit 7-8x rated current.

I once started a 15Hp motor on a 30a 240v breaker. Start current was 120-140a.
 