I'm in the planning stages of my garage build and am planning on having a welder outlet at the back wall and in the front wall. The welder is a Lincoln Powermig 255, and the manual states I could technically get away with #8 wire if it is in conduit and 75° copper, however #6 romex is quite a bit cheaper and easier to run. In looking at the 50A outlets, it doesn't appear I could get away with not needing a pigtail or splice (like a regular 15a wall outlet). As best as I can tell, I will need a connector for 3-#6 wires since a pigtail would be needed. Split bolt connectors appear to only be for 2 wires, and from what I've read is old tech and a pain to use. The polaris connectors look to be pretty optimal, but are quite large and concerned about fitment inside a box (or making sure there is room). Any other connection ideas?
I'm also trying to determine what box size I'll need for the first box containing the pigtail, can someone verify my calcs? My box fill calcs (assuming plastic box) are 6-#6 conductors + 1-#10 ground + outlet = 6x5 + 1x2.5 + 2x5 = 42.5 cu in.
It appears 22.5 cu in is a big as I can get with a single gang PVC box, and a 4" square deep box has 35.0 cu in. Would I have to go with a 2-gang box with a single gang mud adapter plate? From what I can tell the polaris connectors aren't included in box fill calcs but they physically take up room, so I would think they would need to be accounted for especially since there would be three of them.
Also, I'd like to use a single gang outlet cover if possible, which would likely require a mud ring due to the larger box. Is this allowed or does the junction box have to be fully accessible per code?
I'm also trying to determine what box size I'll need for the first box containing the pigtail, can someone verify my calcs? My box fill calcs (assuming plastic box) are 6-#6 conductors + 1-#10 ground + outlet = 6x5 + 1x2.5 + 2x5 = 42.5 cu in.
It appears 22.5 cu in is a big as I can get with a single gang PVC box, and a 4" square deep box has 35.0 cu in. Would I have to go with a 2-gang box with a single gang mud adapter plate? From what I can tell the polaris connectors aren't included in box fill calcs but they physically take up room, so I would think they would need to be accounted for especially since there would be three of them.
Also, I'd like to use a single gang outlet cover if possible, which would likely require a mud ring due to the larger box. Is this allowed or does the junction box have to be fully accessible per code?