I believe I posted in a few other furnace issue threads as a 'me too', but I recently solved my original furnace problem. I thought this would be useful to some, or at least a bit entertaining.
It all started about a year ago, when I started a new job in the New Year, and was working from home for the first time. I set up a workspace in the basement, in the corner of the rec room. It just so happens the furnace room is about 15 feet away. After a few months of getting used to the new job and settling in, I started to notice something strange with the furnace. It was short cycling often. Thermostat calls for heat, inducer motor spins up, burners ignite, then after a few seconds to a minute, the flames extinguish and the whole cycle starts over again. This would come and go, and seemed to have the most trouble in the morning after the house had been warmed up after being set back at night. The furnace is a Nordyne propane, 95% and installed 9 years ago. The heating season was close to over, so I noted to buy a flame sensor and kind of forgot about it.
Last October, I was quickly reminded of the problem when the furnace started coming on (and short-cycling). I had bought a new flame sensor, so I installed it. Same problem. No codes. I called for a furnace service (same guys who installed it). Over the next two months, and close to 10 service calls, they had thrown many different parts at it, and because of a partially clogged heat exchanger, they installed a new furnace, on warranty!
I thought that would be the end of my issues, but I was wrong. New furnace is still short cycling! Not as bad as the original, but still cycles a few times to heat to the set point. They decide the venting is the culprit, although its within spec. They come to install 3" venting but instead cut it off where it goes through the foundation, under the deck. They said they would come back in the spring to install the 3". Again, cutting the vent at the foundation did not fix the problem.
At this point, I was thinking of getting another company to have a look. Could something be wrong with the new furnace? I changed the thermostat with a simple Honeywell, no fix. All that's left is the power? I checked all connections from the panel to the furnace, all tight.
As a last ditch effort, I decided to change out the furnace shut off switch last weekend - this is just a simple light switch on the ceiling near the furnace. Its old, I have never changed it in the 28 years we have lived here. Swapped it out, and ran it. No short cycling - could it be? I tell myself not to get excited, and watch it over a couple of days.
My ears are pretty tuned now to hear the short cycling, especially when working or lying in bed. I have not heard one short cycle since last Sunday - 5 days ago!
My Ecobee thermostat data also suggests the thermostat is not calling for heat as often (or long). The orange bars indicate how long the furnace ran each day. The orange vertical line is when I replaced the switch. I drew in the red and blue horizontal lines to indicate the average runtime (red) and average outside temperature (blue) of the last 4 days only. This helps with comparing the data before and after the switch change.
You can see the furnace has been running less each day, as indicated by the shorter bars to the right of the orange line.

Interestingly enough, the switch ohmed out fine, but after opening up the switch, the contacts had a bit of burn, and one of the screw legs definitely had some oxidation / corrosion.
I suspect the furnace has been short cycling for years and I never noticed it. My guess is the line voltage would dip enough to cause the 24vac to 'brown out', causing the pressure switches to drop out intermittently. It might have also caused the plugged heat exchanger, which definitely would have made the problem worse over time. All this for a 2 dollar switch!


It all started about a year ago, when I started a new job in the New Year, and was working from home for the first time. I set up a workspace in the basement, in the corner of the rec room. It just so happens the furnace room is about 15 feet away. After a few months of getting used to the new job and settling in, I started to notice something strange with the furnace. It was short cycling often. Thermostat calls for heat, inducer motor spins up, burners ignite, then after a few seconds to a minute, the flames extinguish and the whole cycle starts over again. This would come and go, and seemed to have the most trouble in the morning after the house had been warmed up after being set back at night. The furnace is a Nordyne propane, 95% and installed 9 years ago. The heating season was close to over, so I noted to buy a flame sensor and kind of forgot about it.
Last October, I was quickly reminded of the problem when the furnace started coming on (and short-cycling). I had bought a new flame sensor, so I installed it. Same problem. No codes. I called for a furnace service (same guys who installed it). Over the next two months, and close to 10 service calls, they had thrown many different parts at it, and because of a partially clogged heat exchanger, they installed a new furnace, on warranty!
I thought that would be the end of my issues, but I was wrong. New furnace is still short cycling! Not as bad as the original, but still cycles a few times to heat to the set point. They decide the venting is the culprit, although its within spec. They come to install 3" venting but instead cut it off where it goes through the foundation, under the deck. They said they would come back in the spring to install the 3". Again, cutting the vent at the foundation did not fix the problem.
At this point, I was thinking of getting another company to have a look. Could something be wrong with the new furnace? I changed the thermostat with a simple Honeywell, no fix. All that's left is the power? I checked all connections from the panel to the furnace, all tight.
As a last ditch effort, I decided to change out the furnace shut off switch last weekend - this is just a simple light switch on the ceiling near the furnace. Its old, I have never changed it in the 28 years we have lived here. Swapped it out, and ran it. No short cycling - could it be? I tell myself not to get excited, and watch it over a couple of days.
My ears are pretty tuned now to hear the short cycling, especially when working or lying in bed. I have not heard one short cycle since last Sunday - 5 days ago!
My Ecobee thermostat data also suggests the thermostat is not calling for heat as often (or long). The orange bars indicate how long the furnace ran each day. The orange vertical line is when I replaced the switch. I drew in the red and blue horizontal lines to indicate the average runtime (red) and average outside temperature (blue) of the last 4 days only. This helps with comparing the data before and after the switch change.
You can see the furnace has been running less each day, as indicated by the shorter bars to the right of the orange line.

Interestingly enough, the switch ohmed out fine, but after opening up the switch, the contacts had a bit of burn, and one of the screw legs definitely had some oxidation / corrosion.
I suspect the furnace has been short cycling for years and I never noticed it. My guess is the line voltage would dip enough to cause the 24vac to 'brown out', causing the pressure switches to drop out intermittently. It might have also caused the plugged heat exchanger, which definitely would have made the problem worse over time. All this for a 2 dollar switch!