AntonLargiader
Well-known member
This morning I went up to reconnect his furnace which had supposedly been disconnected in order to connect something else. Turns out that wasn't exactly correct; what had happened is that he (via his handyman) had added baseboard electric heat in the basement last winter when the hot water baseboard circuit sprung a leak. One of those new heaters was connected in place of the pool, then disconnected in favor of the pool again in the spring. The furnace was actually connected at all times. In the end I simply swapped back to the heater but this isn't over yet.
Wow, was it ever a good idea to go up there. Here's the arrangement; the meter is basically on the other side of this wall:


Westinghouse panel. Yes, that's a note to "pull both" because separate breakers are used for a 240V circuit. Yes, that box is fed from the line side of the main breaker, and it feeds the other small box via doubled conductors on its line side (and there's no outside disconnect).
In separate news, the circuit for the pool (which is not on a GFCI) is zip-tied to the conduit running on the ground to the hot tub, and then turns and just goes into the concrete. They poured the hot tub slab around it. And BTW that isn't the only exposed UF-B.


So I'm seeing at least the following violations:
Thoughts?
Wow, was it ever a good idea to go up there. Here's the arrangement; the meter is basically on the other side of this wall:


Westinghouse panel. Yes, that's a note to "pull both" because separate breakers are used for a 240V circuit. Yes, that box is fed from the line side of the main breaker, and it feeds the other small box via doubled conductors on its line side (and there's no outside disconnect).
In separate news, the circuit for the pool (which is not on a GFCI) is zip-tied to the conduit running on the ground to the hot tub, and then turns and just goes into the concrete. They poured the hot tub slab around it. And BTW that isn't the only exposed UF-B.


So I'm seeing at least the following violations:
- Illegal feeder tap for small boxes (not in raceway)
- No OCPD for small boxes
- Wrong 240V breaker configuration for gray box
- No clamp where UFB enters panel
- Unprotected UF-B outside
Thoughts?