therealjakeg
Well-known member
Im your gas man, Shoot me some questions from fire pits to heaters, even to your fancy new pool heater that you installed. I have an answer for that item tickling your mind. Enjoy.
1" gas line @ 200' can do up to 135,000 btu or 135MBH thats with the std 7" WC.
Ron
What is a low pressure meter rated to handle? Does the gas co charge to upgrade to high pressure?
Low pressure in NY & NJ is considered under 2 psi ... but most resdiential houses have 1/4 to 1/2 lb gas pressure.
I have never seen the gas co ever put more then 1/4lb 7" WC in a res house.
Thats why gas pipe sizes are sooo important in lwo pressure gas...its all based on volume.
Ron
I’m running a 3/4” gas line to a back yard fire pit using polyethylene gas pipe with meter risers on both ends. Where exactly should the stub out be positioned at the fire pit? In the middle of the pit? Near the edge of the stone blocks? Mid way between the inside and outside circumference rings of the perimeter? Thanks!Im your gas man, Shoot me some questions from fire pits to heaters, even to your fancy new pool heater that you installed. I have an answer for that item tickling your mind. Enjoy
I’d like it away from heat as well but if there is a gas line popping up from the ground outside the fire pit perimeter where you walk, that would be a trip hazard. Plus I’ve never seen visible gas lines near a fire pit. I have to assume it stubs out within the outer perimeter. Maybe a few inches from the edge where holes in the stone blocks are drilled to allow it to come up. There is surprisingly little info online although I haven’t exhausted all search terms yet.Mike,
You've resurrected a thread from 2009 as a way to ask this question. Not the best way to use the forum. In the future, please feel free to start a new thread.
To answer your question...you need to put that riser somewhere where the fire isn't impinging on it or heating it up. The way that riser is made, if you sectioned it with a saw, is the PE pipe comes in horizontally, turns 90-degrees inside the steel shield and goes into a compression joint that transitions it to steel right about where "ground level" is assumed to be by the manufacturer. So, most of the gas carrying pipe inside the riser is plastic. Only the last several inches is steel. If that PE gets hot, it will melt. The outer steel shield is not pressure rated. It just protects the PE inside from being cut by a mower or such.
If it was me, I would have the riser as far away from the actual fire as practical.
Stub it up outside the pit, or inside the wall of the pit, then use a fireplace valve to get you back underground and up into the middle of the pit, or to the side if it is a log lighter.I’m running a 3/4” gas line to a back yard fire pit using polyethylene gas pipe with meter risers on both ends. Where exactly should the stub out be positioned at the fire pit? In the middle of the pit? Near the edge of the stone blocks? Mid way between the inside and outside circumference rings of the perimeter? Thanks!
I’d like it away from heat as well but if there is a gas line popping up from the ground outside the fire pit perimeter where you walk, that would be a trip hazard. Plus I’ve never seen visible gas lines near a fire pit. I have to assume it stubs out within the outer perimeter. Maybe a few inches from the edge where holes in the stone blocks are drilled to allow it to come up. There is surprisingly little info online although I haven’t exhausted all search terms yet.
I’d like it away from heat as well but if there is a gas line popping up from the ground outside the fire pit perimeter where you walk, that would be a trip hazard. Plus I’ve never seen visible gas lines near a fire pit. I have to assume it stubs out within the outer perimeter. Maybe a few inches from the edge where holes in the stone blocks are drilled to allow it to come up. There is surprisingly little info online although I haven’t exhausted all search terms yet.
The type of fire pit will have some influence on this. Also you can buy flex risers. They can be dug in different ways depending on the situation.I’m running a 3/4” gas line to a back yard fire pit using polyethylene gas pipe with meter risers on both ends. Where exactly should the stub out be positioned at the fire pit? In the middle of the pit? Near the edge of the stone blocks? Mid way between the inside and outside circumference rings of the perimeter? Thanks!
I dont understand this comment, Pe risers are metal and only pe at the bottom of the riser. Normally over 24" underground.If you get the steel end of the riser hot, that heat is going right back to the PE which is merely inches away inside that steel protective shell. PE melts at 230 degrees F. Natural gas burns at up to 3600 degrees F.
I dont understand this comment, Pe risers are metal and only pe at the bottom of the riser. Normally over 24" underground
Every riser I have seen the PE goes right up through to the threaded end. The steel is just a jacket to protect the PE.I dont understand this comment, Pe risers are metal and only pe at the bottom of the riser. Normally over 24" underground.
On flex risers, but a hard riser should be usedEvery riser I have seen the PE goes right up through to the threaded end. The steel is just a jacket to protect the PE.
You are wrong. The pe goes all the way up inside the steel jacket, is crimped into a compression coupling in the vertical part of the riser. I’m talking about the “hard” risers. I’ve bought thousands of these for my job and that’s the way they are all made. It actually has to be made that way to prevent the carrier pipe from being subject to corrosion when the jacket leaks water back into the annular space.I dont understand this comment, Pe risers are metal and only pe at the bottom of the riser. Normally over 24" underground.
Fireplaces, have everything from gas valve to plastic under the fireplace. Most outdoor fireplaces, everything is right under the unit. Pe should never be above ground where it can get near the heat, or sun
Hard risers too. I used to sell them.On flex risers, but a hard riser should be used
I see, never used that brand. I have used perfection. I could be wrong, however does not change that most fireplaces, and outdoor pits have a 0 clearance under them. meaning it will not get hot enough to melt.
I didn't sell that brand either, but it was all I could find on the 'net on short order.I see, never used that brand. I have used perfection. I could be wrong, however does not change that most fireplaces, and outdoor pits have a 0 clearance under them. meaning it will not get hot enough to melt.
All empire units have 0 clearance on bottom, left and right. All hookups are directly underneath.
True, If we ever did a custom set up, we always transitioned from pe to cast or copper under ground before coming up out of the ground.I didn't sell that brand either, but it was all I could find on the 'net on short order.
I sold Gastite. Gastite underground was just rebranded from some other manufacturer. I often wondered how many manufacturers there is for CSST and poly underground. When I was i nthe field we used a couple other brands, (which I forget!), but there risers were identical and I believe the Gastite risers were the same.
As for the riser for the fire pit, I would assume it can go right under the pit, bit with no information as to the fire pit he plans on using I wouldn't stick my neck out and assume.
We did a fire pit for a customer. It was some large custom pit. We ran the main gas to a point a few feet from the pit and all the gas controls were at that point. Then we ran a short underground to the pit itself and ran control wire back and for for flame sense and ignition. I remember doing some out of the ordinary plumbing for the gas. The local inspector was involved from start to finish as it was not a normal install.
I worked for a company that did mostly commercial so we ran into some pretty strange installs. Industrial NG at 3.5 and 5 PSI for example, running in 2" threaded mains.True, If we ever did a custom set up, we always transitioned from pe to cast or copper under ground before coming up out of the ground.
This limits where the pe comes out. and gives better flexibility on where we can come out of.
I have only ever used the flexible risers on tank installs, when it came to PE to Flex riser