I have a couple of things to do before I break ground on a new garage. The first project includes burying and stubbing two electrical circuits that go to a greenhouse.

The code I need to comply with is NEC 2011. The only thing I understand is that I need to bury the lines 24" beneath the ground's surface.

Some basic questions;
  • Can I bury the conduit directly in the dirt, or do I need to lay gravel in the trench above/below the conduit?
  • I want to run 2x 20 amp circuits approximately 100 feet; is this just two pairs of 12/2 (with two grounds)?
  • Is there a requirement for a separate ground buried beneath the outbuilding?
  • How large of conduit is typical for two 20 amp circuits like this?

Thanks y'all!
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
You can run pipe right in the ground, usually 18 inches. And you can't run romex in the pipe underground, you will need #12 thhn
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
I believe you may have an issue with two separate circuits if this is a detached building. You may be allowed only one circuit, and then a subpanel for local distribution. Check with how your local jurisdiction considers a greenhouse.

Use wire THWN since this is a wet location.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,274
Location
Modesto, CA
As others have said, u cant run nm-b/Romex underground. U will need either UF-b or thhn wire in conduit.

And yes u may get nailed on the multiple circuits to a detached structure.

If u are just putting in one branch circuit and no subpanel, u dont need a grounding electrode/rod!

The size of conduit is dependent on wire size not circuit ampacity!

With #12 your voltage drop will be about 3.3 %, which is fine but u may want to step upto #10 if u will have any large motor loads like a saw or small compressor!
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
As others have said, u cant run nm-b/Romex underground. U will need either UF-b or thhn wire in conduit.

And yes u may get nailed on the multiple circuits to a detached structure.

If u are just putting in one circuit, u dont need a grounding electrode/rod!

The size of conduit is dependent on wire size not circuit ampacity!

A multi-wire circuit counts as one circuit, and only one circuit is permitted to a outbuilding.

Edit: THHN is for dry locations only, but most is dual rated THHN, THWN, but have seen THHN only conductor...
 