NEC question

willlgord

Active member
Joined
Sep 8, 2011
Messages
43
Location
Fort Mill South Carolina
I'm in the process of setting up an emergency power source for my house and I'm planning to build a small solar power system just for the lights and refrigerator (probably just a 2000 watt inerter with a 400 ah battery bank). The plan is to put the panels, batteries, charge controller and inverter in a detached garage and feed the house with it. Would this be against NEC? I know you cannot have more than one circuit feeding an outbuilding but what about the reverse? I don't want to back feed the garage service since I just want to feed three circuits in the house through a transfer switch. I may also provide a plug in for the generator in case I need it.
This is the transfer switch I want to use, only $99.99 from home Depot
 

Attachments

  • b5f2b6d5-f6ed-48dd-8737-2d737fc7749b_300.jpg
    b5f2b6d5-f6ed-48dd-8737-2d737fc7749b_300.jpg
    9.1 KB · Views: 17
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
There is no simple way to do that.

U want utility power in the garage but also want to use the garage feeder to supply backup power to the house?

U need an interlock or transfer switch on the main service panel to cut utility power.

Problem is that wont allow utility power in the garage.

U will need a seperate feed for the backup supply.
 
OP
W

willlgord

Active member
Joined
Sep 8, 2011
Messages
43
Location
Fort Mill South Carolina
No, I do not want to use the garage feeder, I want to run a separate circuit in a separate underground conduit back to the transfer switch in the house for solar/emergency power. Is it legal?

The transfer switch would be installed next to the main panel to isolate the three circuits I want to power up from the grid.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I don't see why not, as long as the transfer cuts out the main so no power from the solar can back feed to the service.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
No, I do not want to use the garage feeder, I want to run a separate circuit in a separate underground conduit back to the transfer switch in the house for solar/emergency power. Is it legal?

The transfer switch would be installed next to the main panel to isolate the three circuits I want to power up from the grid.

Aww ok. Then that would be fine. U didnt mention anything about a separate feed.

Move the 3 circuits to the transfer switch and connect generator to transfer switch via separate feeder.
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
I think you can make the case that a 225.30(A) exemption applies, allowing you to have multiple feeds to the outbuilding. You would need a permanent sign/directory at each disconnect location showing other feeds and what they serve (225.37).

For grid-tie solar, I'd argue that the grid-tie is a feeder, even though the logical flow of electricity is in the other direction, the electrical danger is the same from someone who "cuts the power" to the garage and assumes that all the power lines are then dead. That's why 225.37 exists.
 