Need A Little Help Sizing Wires ** SOLVED!
For most of the electrical jobs a home and shop owner is faced with I am a pretty capable electrician; I respect electricity, I understand the basics, I am **** about the details, I know when I need help, and I am not cheap.
After a bit of on line research and consulting my Ugly's Electrical Reference I still need a bit of wire sizing assistance. With the current price of copper I am reluctant to over engineer a project that requires long runs. But I don't want to undersize either.
Here is my situation. I have 100 amps at the sub panel in my shop. I am installing a 3.5 ton "package" heat pump. The run from the sub-panel is about 75 feet. I plan on using NM cable. I can surface mount this cable if necessary but would prefer to run it inside walls that will eventually be insulated.
The unit specs call for 40 amps of protection and 29 amps run. Can I use NM 2/10/WG or will I need NM 2/8/WG?
The unit has three 5 KW heat strips with one 30 amp and one 60 amp breaker. I know that I do not have sufficient amps at the panel to support this load and only plan to wire up the 30 amp strip. Again, the question is can I use NM 2/10/WG or will I need 2/8/WG.
If I am reading my references right my situations are right at the limit of #10. What would you use?
For most of the electrical jobs a home and shop owner is faced with I am a pretty capable electrician; I respect electricity, I understand the basics, I am **** about the details, I know when I need help, and I am not cheap.
After a bit of on line research and consulting my Ugly's Electrical Reference I still need a bit of wire sizing assistance. With the current price of copper I am reluctant to over engineer a project that requires long runs. But I don't want to undersize either.
Here is my situation. I have 100 amps at the sub panel in my shop. I am installing a 3.5 ton "package" heat pump. The run from the sub-panel is about 75 feet. I plan on using NM cable. I can surface mount this cable if necessary but would prefer to run it inside walls that will eventually be insulated.
The unit specs call for 40 amps of protection and 29 amps run. Can I use NM 2/10/WG or will I need NM 2/8/WG?
The unit has three 5 KW heat strips with one 30 amp and one 60 amp breaker. I know that I do not have sufficient amps at the panel to support this load and only plan to wire up the 30 amp strip. Again, the question is can I use NM 2/10/WG or will I need 2/8/WG.
If I am reading my references right my situations are right at the limit of #10. What would you use?