Need a little verification

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
I have a 240 20 amp circuit that runs to my attached carport
Original owners had it there to run a small generator
I have been using it for my air compressor but no longer need it since I have a garage now
Would it be ok to swap the dp breaker with a single pole 20 amp and of course a 20 amp receptacle
Haven’t looked yet but assuming it has 4 wires, one of which would not be used
Should be 12 gauge wire
Anything wrong with 12 gauge wire for a 120 volt circuit
340b5df57291d0f68187f1a0ed1df8ab.jpg




Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!

38Chevy454

Well-known member
Joined
Dec 26, 2006
Messages
4,036
Location
Cincinnati, OH
You can actually split into two 20A 120v circuits. Need two breakers of course, one for each leg of the 240v circuit. Just ensure the old wiring has a neutral for each 120v leg. Some older 240v circuit only have the 2 hot legs and ground.

Sent from dumb operator on a smart phone
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Man, out of the 2 brain cells I have left only 1 was working
on the 12 gauge for 20 amps LOL ��
Good idea on doing 2 receptacles
Thanks
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,928
Location
Niagara Region, Ontario, Canada
You can actually split into two 20A 120v circuits. Need two breakers of course, one for each leg of the 240v circuit. Just ensure the old wiring has a neutral for each 120v leg. Some older 240v circuit only have the 2 hot legs and ground.

Sent from dumb operator on a smart phone

wrong information
he can get 2 120 circuits only if there is a neutral, and must use a double pole breaker . probably no neutral exists for this .
todays wiring, a 240 circuit only requires 2 hots and a ground . no neutral required.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
I can almost guarantee that there is not 4 wires ran to the box. It has a black, white, and ground. The white will have been reidentified as the second hot.

You can still convert to 120. Just move the white wire from the breaker to the neutral bus and install a single pole breaker on the black wire.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I can almost guarantee that there is not 4 wires ran to the box. It has a black, white, and ground. The white will have been reidentified as the second hot.

You can still convert to 120. Just move the white wire from the breaker to the neutral bus and install a single pole breaker on the black wire.

This is my bet too! People don't generally run a 4 wires when they only need 3. Except if they're Garage Journal members. :lol_hitti
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Looked at receptacle a few minutes ago
Been busy building a small deck/stoop on the side door of my home
Bert you are spot on buddy
Black white and ground
I’ll go to supply house Monday and get what I need
Thanks for everybody’s help
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
OP said, "I have a 240 20 amp circuit that runs to my attached carport
Original owners had it there to run a small generator
"

This is scary!
 
To avoid these ads, REGISTER NOW!
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
I assuming they were backfeeding when power went out
Don’t know if it was small but 20 amps isn’t a whole lot
The dp breaker in the panel has generator wrote on it
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
Chances are the neutral is bonded in both the generator and the house panel. Neutral current will flow on the ground. Pretty sketchy set up.
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Bert
What exactly is bonding in the panel
I’m just picturing black wire, white wire both connected to the Dp breaker and of course ground


Sent from my iPhone using Tapatalk
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Bert
What exactly is bonding in the panel
I’m just picturing black wire, white wire both connected to the Dp breaker and of course ground


Sent from my iPhone using Tapatalk
In the main panel (or first point of disconnect if the main panel isn't the first point) the neutral and ground are connected (bonded), after that point they should be separate.

I wonder if that was originally a normal 120v outlet and someone "repurposed" it into a way to improperly backfeed from a generator.

Sent from my SM-G965U using Tapatalk
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
That’s possible
Was in Home Depot today
Picked up a levitron 20a gfci outdoor receptacle
Should I have gotten a different brand
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
I didn’t think about it Bert but I believe I have some in the garage


Sent from my iPhone using Tapatalk
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,280
Location
The romantic hills of central Umbria, Italy,
Leviton is a good brand - been using their stuff forever. Just don't trust the press in terminals - use the screw downs.

This is my bet too! People don't generally run a 4 wires when they only need 3. Except if they're Garage Journal members. :lol_hitti

GJ members would not only run 4 wires, they'd run an extra length of 10-3 and put in a length of conduit as well as plumb it with copper for the eventual air you'll want there... "just in case".
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
I did but I didn’t get one for a gfci
Hooked it all up today. Works fine
I did have to do something that some of you might frown on
The white wire wasn’t long enough to reach neutral bar so I had to wire nut a 10” piece
That’s probably against code but oh well I don’t think it will cause any problems
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
I did have to do something that some of you might frown on
The white wire wasn’t long enough to reach neutral bar so I had to wire nut a 10” piece
That’s probably against code but oh well I don’t think it will cause any problems

Works fine. I would have done the exact same thing.
 