CGT80
Well-known member
I need to add a magnetic starter to my 5hp compressor and want to make sure the amperage is correct for my motor. I'm not sure how close to the running amperage these should be.
Baldor L1508T
5hp 1725 rpm
208-230 28.5 amps
1.15 service factor
28.5x1.15=32.77 amps max
I run my pump up to 170 psi and I think it maxed out right at 30 amps as it reached full pressure. I need to recheck it to be sure and also because I just replaced the bearings, the start switch, and cleaned up the centrifugal switch, which was not working smoothly.
The other day, it tripped the breaker a couple times and it has not done this at all since I got it a year ago. The bearings were a bit rough.
The feed to this is small and I should probably re-run this line. It is a 30 amp breaker and #10 from the garage sub panel. The motor does not have a safety or reset and without a magnetic starter there is no way I'll run a larger feed until I do.
The startup amperage was 167 amps, last time I checked.
Here is what I was considering: https://www.amazon.com/dp/B004PHB5U8/?tag=atomicindus08-20
It has a b-40 heater element and 30 amp contactor.
I have read and google searched GJ for more detailed info on the heater element and I used to a lot of electrical work and trouble shooting when I was in the construction trades, so residential and small commercial electrical is nothing new to me.
Is the heating element a one shot deal, like a fuse, or do they "reset" to be used again? How close to the max amperage of the motor should they be?
I have seen some that were electronic and adjustable but the $60 units don't have the best reviews and Square D is a good name brand, but there are not a lot of options on Amazon. Other suppliers are ok and I could hit up an electrical supplier if needed.
Luckily, the old square D pressure switch that is on my compressor is well built and has big contacts (I dressed them when I got it) but I want to get this setup the right way and protect an expensive motor and really nice pump.
Thanks
Baldor L1508T
5hp 1725 rpm
208-230 28.5 amps
1.15 service factor
28.5x1.15=32.77 amps max
I run my pump up to 170 psi and I think it maxed out right at 30 amps as it reached full pressure. I need to recheck it to be sure and also because I just replaced the bearings, the start switch, and cleaned up the centrifugal switch, which was not working smoothly.
The other day, it tripped the breaker a couple times and it has not done this at all since I got it a year ago. The bearings were a bit rough.
The feed to this is small and I should probably re-run this line. It is a 30 amp breaker and #10 from the garage sub panel. The motor does not have a safety or reset and without a magnetic starter there is no way I'll run a larger feed until I do.
The startup amperage was 167 amps, last time I checked.
Here is what I was considering: https://www.amazon.com/dp/B004PHB5U8/?tag=atomicindus08-20
It has a b-40 heater element and 30 amp contactor.
I have read and google searched GJ for more detailed info on the heater element and I used to a lot of electrical work and trouble shooting when I was in the construction trades, so residential and small commercial electrical is nothing new to me.
Is the heating element a one shot deal, like a fuse, or do they "reset" to be used again? How close to the max amperage of the motor should they be?
I have seen some that were electronic and adjustable but the $60 units don't have the best reviews and Square D is a good name brand, but there are not a lot of options on Amazon. Other suppliers are ok and I could hit up an electrical supplier if needed.
Luckily, the old square D pressure switch that is on my compressor is well built and has big contacts (I dressed them when I got it) but I want to get this setup the right way and protect an expensive motor and really nice pump.
Thanks