I got to this post late, but I see a couple of downsides...though not what I'd call showstoppers.
If it's a natural gas heater, you need to look at the pipe size requirement for a 250,000 btu hour per load and insure that you can do that in a feasible way. I'm guessing it would have a 3/4" or 1" inlet, but depending on the length of the run, you might have to use larger pipe. In Evansville, you'd be on Vectren South. I'm pretty sure they supply you with 7 inches w/c gas supply. Your meter is likely rated for about 275,000 total BTU's per hour...so if you notice your house's furnace doesn't want to run right, you'd need to call Vectren and ask them for a bigger meter.
You are also going to have to supply a larger flue. If it's a B-vent...it might be what? 6" Diameter? Is that a problem for where you are going to install it.
The other issue would relate to efficiency. An 80% efficient 250,000 btu furnace wastes 50,000 BTU's per hour. At today's gas rates, that's about 60 cents per hour of burner time out the flue. The burner will run less than a smaller furnace, evening it out some...but I know my house used to have KILLER gas bills before I jerked out the 250,000 BTU furnace and put a 125,000 BTU furnace in its place.
The other thing I was going to point out is this. If you are only going to run it when you are out there, and can get the gas line you need and the flue you need...and the price is right, I don't see anything wrong with the idea. If you are going to be running it all the time, I'd suggest going with a new high efficiency furnace. It'll pay for itself rather quickly.
Good Luck!
Phil