Need electrical help
K
Kybound
Yes the gfci tripped and the 3 outlets downstream were off, but the gfci was still hot. Hit the reset all call on.
mike93lx
Richmond, VA
If they are tripping still, they are either faulty or there is a problem with something plugged in. Don't bypass or remove them because they are annoying.
If everything is good, you should be able to forget that they are there. I can't even remember the last time I had to reset one
Ok I did what you said and with the ground off it did not trip. When I was loosing the ground terminal I had the drill on forward and it tightened down some more. Would a loose ground have caused this problem?
No a loose ground will not cause this problem.
GFCIs dont care about what’s going on with the ground wire. This is because they only measure current on hot and neutral.
K
Kybound
Now on another circuit the tree outlets downstream are working and just the gfci tripped.
Terry D
St. Louis, MO.
I just read you earlier post, you gave rhis crazy stuff happening on the other gfci circuits. How do you have them wired. You should have 2 blacks and 2 whites to each gfci. And there is also a load and line side
Sent from my SM-G960U using The Garage Journal mobile app
yatg
Southern Oregon
All the 240 are homeruns. One circuit to one plug. I have three separate 20 amp 240 plugs and it does this on every one.
Current from dedicated 240v circuits should not bleed over onto separate 120v circuits. Do you have any junction boxes between the panel and the 240v receptacles where wires could be crossed?
K
Kybound
Sorry guys been cutting grass. Nothing is tied to any 240 circuit they are all breaker to outlet. As far as wiring the gfci, put hot and neutral on bottom of the plug the load side the top to a pigtail to feed the next outlet. I have one of the circuit testers and both lights light up like it is wired correctly. As far as the original problem I can't get the thing to trip now. But didn't fix anything and I do t believe in a fluke. It will happen again.
K
Kybound
No I dont believe so. Guys I appreciate all your help. As of now I'm not having any issues. Will let you know if it happens again.
dave*99
Coastal NJ
Does your tester have a button to test a GFCI? Test all GFCI and downstream GFCI protected receptacles with that type tester.
Terry D
St. Louis, MO.
You have it wired wrong. The load side should go to the receptacles down stream. The power coming in should fo to the line side. There should be no pigtails