Trying to help my son and I am definitely no electrician. He lost his power and after it came back on he has no hot water. It is an electric water tank. It runs on 240 but he's only getting a 130 volts from that line now. Anyone have any idea what could have happened?

Side not we just installed a new electric water heater and still no hot water. Really appreciate any help.

Also it's a fuse panel not a breaker panel.
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Do you have a multi-meter? check the main panel to make sure you have 240v line to line. then test breaker lugs, with breaker on, for 240v.

BTW its 240v not 220v
 
Last edited:

Super Mech

Well-known member
Joined
Feb 19, 2011
Messages
1,806
Location
Bronx,NY
Check both breakers for the heater. Then check if you 110v on both legs coming into the main panel. Sounds like one leg is still out.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,501
Location
Omaha, NE
Check the fuses...if necessary swap from a working circuit

Sent from The Garage Journal mobile app
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Check the breaker box-

240 is 2- 120's and a neutral. Fed with a 2 pole breaker

fixed it for you :thumbup:

Check both breakers for the heater. Then check if you 120v on both legs coming into the main panel. Sounds like one leg is still out.

It should be one breaker feeding the water heater and the heating elements dont care about 120v. The proper way to troubleshoot this is by metering line to line not line to neutral

.
How are you measuring the 130v from each leg(wire) to ground or across the 2 legs?

how does one get 130v on a 240/120v split service? how does one get 130v testing from leg to leg? :headscrat

youre just confusing the OP who has no electrical experience...
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Don't know ask the OP he's the one that got the 130v measurement.

Did you even read his post?

yes i read the post.

you asked him if he was getting the 130v "across the 2 legs".

that is impossible to do. you cannot get 130v from 2 ungrounded conductors in a split phase service
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,046
Location
Southeastern Pa
yes i read the post.

you asked him if he was getting the 130v "across the 2 legs".

that is impossible to do. you cannot get 130v from 2 ungrounded conductors in a split phase service

So I guess asking where he got the 130v reading from is pointless in your world since it isn't possible?
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
yes i read the post.

you asked him if he was getting the 130v "across the 2 legs".

that is impossible to do. you cannot get 130v from 2 ungrounded conductors in a split phase service
I can think of a couple ways one might see 130v.
One way would be a super cheap inaccurate meter thats off by a good margin. I think you can get meters like that from horrible frieght. This of course would have to be measured from hot to ground.
Second would be a fuse on one leg that has failed(or possibly the fuse holder) and it is still making just enough of a connection to pass a few volts through.

A few years ago we had a gentleman come to us wanting to buy a "good" water heater as the 3 he had gotten from the box stores were all junk, turns out he was measuring to ground with it hooked up and seeing 120v on each leg, he actually had a blown fuse the whole time.

Sent from my SM-G965U using Tapatalk
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
You've got a bad fuse

Check this first as Bert said. It is the most logical first step versus doing all the other things people are saying to do.

All that may have happened is that one of the two fuses blew out and a simple check of both fuses will let you know in seconds if this is your problem.

Always start with the easy things first.

Jim
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,907
Location
Coronado, CA
If you have no idea of what your problem is; you can call your electric utility and see if they will check it for you.
 

Davegvg

Well-known member
Joined
Jul 21, 2018
Messages
285
Location
Corona Ca.
an oven w/ 120v controls and lights would get a 4-wire branch circuit connection.

but what does that have to do with a 240v water heater which has no 120v controls? :headscrat :dunno:

I'm not the one talking about 120 V controls.

The question was (If 240 has no neutral) where does the neutral come from in that example.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
I'm not the one talking about 120 V controls.

The question was (If 240 has no neutral) where does the neutral come from in that example.

Huh? Youre the one that asked about them in post #21

Your question has no bearing on the subject and only muddies the waters.
 

Davegvg

Well-known member
Joined
Jul 21, 2018
Messages
285
Location
Corona Ca.
Huh? Youre the one that asked about them in post #21

Your question has no bearing on the subject and only muddies the waters.

Never said anything about "120V controls" but should probably have taken it off line vs talk to alfred about his statement which seems to conflict with yours.

I'll start my own thread.
 