To avoid these ads, REGISTER NOW!

Need help confirming Modine btu for garage

jzinckgra

Member
Joined
Nov 17, 2018
Messages
7
Location
Maine
We built our house 6 yrs ago with radiant heat running off a baxi ht380 propane boiler. The builder ran pex to the garage for future addition of hydronic heater. Our garage is insulated with spray foam with sheetrock 10' ceiling. Sqft is 800.

In looking at heat load calculators it says if we want to heat up to 60f we'd need a 46,000btu Modine. Does this sound right? I'm not sure if we should get copper or aluminum version heater.

Local plummer will do work and it looks pretty straight forward. Anything else to consider? Thanks

Sent from my Pixel 2 using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
J

jzinckgra

Member
Joined
Nov 17, 2018
Messages
7
Location
Maine
I'm getting different results using two different calculators. One says I need 30kbtu while another says 63k.

Sent from my Pixel 2 using Tapatalk
 

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
713
Location
Southern Alberta
One quick and dirty calculation we use is 10 watts/square foot. So in your case that would give you about 30000btu.

A few "buts" on that: 10 foot ceilings may need a little more and my suggestion is based on a well insulated and sealed space.
 
OP
J

jzinckgra

Member
Joined
Nov 17, 2018
Messages
7
Location
Maine
Garage is pretty tight. Spray foam walls, but a little leaky around garage doors. Any issue going with Modine 45kbtu over the 33? I'd rather be over than under and pretty certain our boiler can handle it

Sent from my Pixel 2 using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
J

jzinckgra

Member
Joined
Nov 17, 2018
Messages
7
Location
Maine
I've asked our plumber to go with the 47K BTU unit. I do see Modine's specs say that the 47K BTU is if you're using steam. with hot water, it'll only put out ~34k BTU. Still should be ok.

Our boiler is only ~15' away from where heater would be. Would it still be advised to use an aquastat? I don't really care if the fan blows cold air for a few minutes.
 

R.Beans

New member
Joined
Jan 2, 2017
Messages
3
I was advised by my HVAC company to do a 45,000 btu for a 30x40x10.. went with a Reznor UDAS. Time will tell.
 