Need Help Determining if 1/2" Gas Line is Good Enough

Sygheric

New member
Joined
Mar 7, 2014
Messages
2
As soon as the weather breaks, I'm going to start my 28'x32'x10 garage (pole barn) project. I'm going to insulate the walls and ceiling, finishing with drywall. I want to heat with a 45k btu forced air furnace. The issue is, I don't know if a 1/2" line at 120' will be enough gas pressure for the furnace to work properly. Any suggestions?
 
To avoid these ads, REGISTER NOW!

koditten

Well-known member
Joined
Apr 10, 2008
Messages
5,528
Location
Midland, Michigan
You will be running 1 inch and reducing it as it enters the building. I got no issue running my 75k furnace. I have 185' between the house and shop.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,417
Location
N CA
Let's see....I've got the 2012 edition of NFPA 54 here in my lap and using polyethylene plastic pipe at 125' with 1/2, 3/4 & 1" you can expect 51,103 & 185 kbtu respectively at .5" pressure drop with NG. With fittings and the expectation of adding load sometime in the future I'd do 1". Better to have the extra capacity and not need it than need it and not have it!
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Remember once he gets there with the pex, then changes to iron, first elbow will need to be calculated as a pressure drop and every one after that. Even the iron through the building will be a slight pressure drop due to rough interior verse Pex.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,368
Location
Beautiful Southern Maryland
I don't understand why you would not just call your gas company and ask them ???? I am thinking about doing the same with my detached garage and Washington Gas will be who I call. I would think they would gladly give you the correct answer and I would hope they would be the experts in the matter ?
 