need help on service wire size and type
Bigfork G
I'm getting ready (hopefully) to start on a 24x36 work shop. The shop is 450 feet from the meter and transformer. The ground is rocky so conduit is a must.
What size and type of wire do I need? From what I'm reading the mobile home service wire can not be used inside of conduit, it become a wet environment, is this correct?
The electric provider will not go more than 200 feet then we are talking additional transformer, wire, meter panel, labor and a price tag of over $8,500.00
Almost forgot.
For my needs I'm looking at 90 amps but would like to be safe and have 125.
pattenp
Virginia - USA
Almost forgot.
That is not correct. MHF can be direct buried or placed in conduit. It does have to be in conduit inside of the structure.
Edit: Oh, I suggest using 4/0-4/0-4/0-2/0 MHF
Bigfork G
Do you how many amps the 4/0 4/0 4/0 2 could carry that distance?
JoeFin
NorCal - where the Rednecks Race
Not a big fan of Multi-conductor cable in conduit, Direct Burial nor aluminum wiring.
Both seem great when you first crunch the numbers - but cost over time they are real big losers. THHN in PVC Ridged Conduit has been an Industrial / Commercial standard for a pretty long time for a reason
pattenp
Virginia - USA
The 4/0 @ 450' with an 80A load should be right at 3% VD and 120A load at about 5% VD. 3% is recommend by the NEC, but 5% should be the max.
Also there is absolutely nothing wrong with using the MHF in conduit and aluminum is used as service feeds by POCO's all the time. For a 450' run copper is going to cost a small fortune. The MHF if installed correctly and in conduit, will last way beyond your life span.
OP what loads will u have?
U made a bunch of claims with no evidence or fact to back up your claims.
So why is cable such as MHF a "real big loser"? :dunno:
Bigfork G
Diesels right at 90 amps if I have everything running at once, not going to happen though I only have 2 hands.