I believe the conduit is metallic and hopefully rigid if in the pour. It also has a metallic bushing on it.
If it were pvc, then it's AFU. They would have needed to pull an egc.
Looks like the conduit passes thru a concentric ko. It should have a bonding bushing on it.
I thought bonding bushings were only required on 480v and above.
Let’s face it most churches get electrical work done by good church members. They might not be the most qualified but think they are.

Now back to the original problem..............
Did you do what ARD suggested in post 49?
When you measured the original voltages, was the stove disconnected from recept?
Did you ever measure the voltage between neutral block and enclosure (grd) at the panel?
No. I didn’t try that.
I snapped a couple of shots of the service entering the building from under the street.
![]()
![]()
If you had to start this thread you have no business in that cabinet.
Go back and read the thread, the solution (s) have been posted. Better yet call and electrician, maybe you can get one to donate the labor.

One note about that cabinet- its odd to see paralleled conductors on the top phase leg that are different sizes. Should be the same size.
One note about that cabinet- its odd to see paralleled conductors on the top phase leg that are different sizes. Should be the same size.
Let’s face it most churches get electrical work done by good church members. They might not be the most qualified but think they are.

That's the exact reason why you had no business opening it up in the first place.I figured I could just probe around with my Fluke meter in that supply cabinet until I find the right voltage and tap right into the lugs there.

The building was a flooring and rug store for years before the church got it cheap. That’s why the overkill on the electrical supply.
I didn’t get anything else done there yet because I didn’t have the time to meet anyone there and spend the day. The oven is not a priority for them, so I didn’t make time to get it straightened out.
I figured I could just probe around with my Fluke meter in that supply cabinet until I find the right voltage and tap right into the lugs there.
Sent from my iPhone using Tapatalk
The building was a flooring and rug store for years before the church got it cheap. That’s why the overkill on the electrical supply.
I didn’t get anything else done there yet because I didn’t have the time to meet anyone there and spend the day. The oven is not a priority for them, so I didn’t make time to get it straightened out.
I figured I could just probe around with my Fluke meter in that supply cabinet until I find the right voltage and tap right into the lugs there.
Sent from my iPhone using Tapatalk
Not necessarily
My old company did a church with wood studs and MC cable.
The volunteers took care of the drywall, and used 3" #8 screws to hang 5/8 on every 2x4 wall in the place.
We had to replace all but 1 piece of the cable, and it was necessary to tear out all the bottom sheets of drywall on 1 side of the wall![]()
Come on brothers, I thought it would be pretty clear that I was joking with that last post about poking around in that three phase cabinet with my DVM.
I am grateful for everyone’s input on this thread. I appreciate your insightful advice.
Sent from my iPhone using Tapatalk
If arc flash doesn't motivate you, google: notre dame.
You've gained enough knowledge here to now properly explain the problem(s) to an electrician. This job has grown way to big in scope and danger for you.