Need help with air compressor

Tech89

Well-known member
Joined
Nov 9, 2013
Messages
416
Bought a air compressor, here's a link to said compressor http://www.industrialairusa.com/prod_detail.php?model=IV5076055&cat=3
I need to wire it, but I'm unsure what to use for wire. My last compressor was wired with 10-3 SOW cord to the outlet I believe, I can't remember exactly. Does this seem correct? I wired it myself, I just cart remember what I used. I like the SOW because it was nice a flexible. Thanks in advance for everyone's help.

-Pat

Sent from my SAMSUNG-SM-G891A using Tapatalk
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I looked through the manual and it doesnt list the HP whoch is needed to size the wire and circuit.

Can you post a pic of the nameplate.

If it is truly 5HP(its listed as 5RHP), then it must be hardwired and will
Need 35a rated wire- #8/2 NM-b or #10 THWN.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Motor loads have different NEC requirements as to how they are to be wired. The HP is used to cross reference a table in the NEC code book to get the amps. Plus the nema plugs most people will likely try to use are only rated up to 3 - 3.5 HP. So 5HP needs to be hardwired, no plug and outlet.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Why is that? My electric stove is rated at more than that and it has a pigtail. Could he not utilize a setup like that?

A stove is different than a motor because of the HP rating.

But im not sure why youre referencing a pigtail.

do you mean cord and attachment plug?
 

Notgrownup

Well-known member
Joined
May 5, 2014
Messages
5,869
Location
Snow Hill NC
I used a #8 cable and wired mine to a plug with a matching receptacle in the wall, this way I can move it easily if I want.
 
OP
T

Tech89

Well-known member
Joined
Nov 9, 2013
Messages
416
I guess I'll be running another line from the breaker box, I already have 2 220 outlet coming out of it haha.
 
Last edited:
OP
T

Tech89

Well-known member
Joined
Nov 9, 2013
Messages
416
I used a #8 cable and wired mine to a plug with a matching receptacle in the wall, this way I can move it easily if I want.
That's exactly what I wanted to run a plug and outlet. I did that with my last 5 HP 2 stage compressor, I used a Nema plug as pictured. I wasn't aware that this wasn't okay.

-Pat
f4fa8c454394d776d86d4f9377e478f1.jpg


Sent from my SAMSUNG-SM-G891A using Tapatalk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That's exactly what I wanted to run a plug and outlet. I did that with my last 5 HP 2 stage compressor, I used a Nema plug as pictured. I wasn't aware that this wasn't okay.

-Pat
Sent from my SAMSUNG-SM-G891A using Tapatalk

NEC is all about safety and it's not that the plug can't handle the amperage it's about pulling the plug on a motor that's 5HP and greater under load because of the potential of arcing and shooting sparks into you eyes. Technically a plug is a disconnect and a standard nema 3HP plug is not approved as a disconnect for a 5HP motor because it does not provide any arc shielding. A pin and sleeve plug is what needs to be used but they are expensive.
 
To avoid these ads, REGISTER NOW!
OP
T

Tech89

Well-known member
Joined
Nov 9, 2013
Messages
416
NEC is all about safety and it's not that the plug can't handle the amperage it's about pulling the plug on a motor that's 5HP and greater under load because of the potential of arcing and shooting sparks into you eyes. Technically a plug is a disconnect and a standard nema 3HP plug is not approved as a disconnect for a 5HP motor because it does not provide any arc shielding. A pin and sleeve plug is what needs to be used but they are expensive.
Would you be able to link a few. I don't know that I've seen those before.

-Pat

Sent from my SAMSUNG-SM-G891A using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Sorry, yeah I googled it afterwards. Those are fairly spendy.

-Pat

Sent from my SAMSUNG-SM-G891A using Tapatalk



"Fairly spendy"? They are ****** expensive, I have them on my MillerMatic 251.

DSC02893.jpg
 
Last edited:

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
It would be great if we had a sticky for compressor wiring!

I was just given a 240V 15A compressor. Although 15A doesn't show up in the NEC table, it seems like about 2.5 HP? It has no plug but it was probably on a 6-20. As I have a 6-20R about fifteen feet away but out of sight, it would be great if I could just make a cord for that distance. Hardwiring is an option but it seems like such overkill for this, which almost certainly came with a 6-20. Cooper says 6-20 is rated at 2HP. How does NEC treat this? To get to 3HP I need to go to 6-50 and then there are wire size and breaker issues, right?

Is a 6-20 legit for this compressor? Nameplate below. Oh, and there's a big "6 HP" sticker on the compressor but fortunately not on the nameplate. :)

IMG_7814.jpgIMG_7815.jpg
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
It would be great if we had a sticky for compressor wiring!

I was just given a 240V 15A compressor. Although 15A doesn't show up in the NEC table, it seems like about 2.5 HP? It has no plug but it was probably on a 6-20. As I have a 6-20R about fifteen feet away but out of sight, it would be great if I could just make a cord for that distance. Hardwiring is an option but it seems like such overkill for this, which almost certainly came with a 6-20. Cooper says 6-20 is rated at 2HP. How does NEC treat this? To get to 3HP I need to go to 6-50 and then there are wire size and breaker issues, right?

Is a 6-20 legit for this compressor? Nameplate below. Oh, and there's a big "6 HP" sticker on the compressor but fortunately not on the nameplate. :)

IMG_7814.jpgIMG_7815.jpg

Thats probably a 3HP since NEC lists the FLC for a 3HP at 17a. FLC is different than FLA in that FLC is the max current a 3HP motor would have under the NEC. Most true 3HP motors will be less than 17a.

Re: sticky I plan on adding a compressor wiring post to my electrical FAQ sticky when i get the time.
 