I have all the settings set the way they should be. Is it possible that pc board that those wires go through is bad? It does not have aux heat we live in Florida still have not needed the heat yet. But we will
Is this a split unit with outside heat pump condenser?
Put thermostat in system test.
Set test function to 1 in cooling mode so compressor and fan ON.
Reversing valve should be energized. and it should cool.
Now set test function 3 in heating mode so compressor and fan ON.
You should get heat if function 170 is set to heat pump during set up,
Test orange wire if you do not have 24VAC (from outdoor unit)
Reversing valve should not be energized and should get heat.
If not, thermostat could be bad or there is a wire issue.