ard
Basically 4 transformers, beginning and end of each of the 2 runs. Up to 480v, down to 240v, subpanel, rest of circuit?
Two; one up...one down. ebay will be your friend.
The rating will be in kva. if, say, you want 20A, then 20X120=2400=2.5kva.
And therein lies the key. at 480V in the long run, you only need **5 Amps** (5x480=2400) to supply that 20A@120. And the voltage drop due to pushing 5 A in #8 is far less.