So....

I've always been curious about what "ground" and not Neutral, actually refers to here. To me, the fact that "ground" is a rod driven into the ground is coincidental. You're using this rod as a connection to what? Another rod (through the rock and soil) at the transformer pole that has a connection to the source? Power is always trying to return to its source correct? Is just doesn't go randomly into the earth when there's a fault.
The power plant also has a huge grounding rod I believe.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
So....

I've always been curious about what "ground" and not Neutral, actually refers to here. To me, the fact that "ground" is a rod driven into the ground is coincidental. You're using this rod as a connection to what? Another rod (through the rock and soil) at the transformer pole that has a connection to the source? Power is always trying to return to its source correct? Is just doesn't go randomly into the earth when there's a fault.

People are always confused about grounding/EGCs and grounding electrodes/rods/ufer, etc....i think this is because they share a common name....

Grounds/EGCs are for grounding the metal chasssis of equipment in case of an ungrounded hot leg short to the chassis and they provide a low impedance fault path so breakers can clear the fault.

Grounding electrodes on the other hand are for grounding lightning, providing a reference to ground and to help limit voltage potential because of contact with higher voltage lines or surges!
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,246
Location
SE MI
Grounds/EGCs are for grounding the metal chasssis of equipment in case of an ungrounded hot leg short to the chassis and they provide a low impedance fault path ...
... and this really goes back the very early days of home electrification.

From the 1900s through 1950-60ish, homes only had hot and neutral AND most household appliance had metal cases. A short from hot to the case could seriously hurt/kill someone if they became the path to ground.

10-20 years after ground wire became common in household wiring, many (most?) handheld/countertop appliances started using plastic cases/housing. Then there was the invention of "double insulation" (Class II) appliances which do not require a ground.

I always get a chuckle when I look at a plastic housed DC computer power supplies that have a 3 wire cord and plug !
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
... and this really goes back the very early days of home electrification.

From the 1900s through 1950-60ish, homes only had hot and neutral AND most household appliance had metal cases. A short from hot to the case could seriously hurt/kill someone if they became the path to ground.

10-20 years after ground wire became common in household wiring, many (most?) handheld/countertop appliances started using plastic cases/housing. Then there was the invention of "double insulation" (Class II) appliances which do not require a ground.

I always get a chuckle when I look at a plastic housed DC computer power supplies that have a 3 wire cord and plug !


Yeah i dont know why manu. do that...must have some importance, like surge suppression maybe?
 