gpiggaz
Well-known member
I have a situation where I need to feed a sub panel in a detached garage, However, I discovered there are no spaces left in the main to put a new breaker, and all but one of the breakers in the current main ( Siemens) are dual breakers. So it's not like I can clear out the 2" I need to put in the 60 Amp breaker to feed the detached garage sub panel buy using dual breakers
We have done the load calculations (200Amp main service) and we're ok with the additional loads of the garage- Already have the permits in hand to do the work, but hadn't counted on a completely full panel.
I have an idea- can I put in a new sub panel at the main house, and feed it with a 80 amp breaker and ( or there about's) to it, using 4AWG CU for the 2 ft between the main and sub unless it needs to be more than 80Amps. Move 4 20 amp circuits over to the new sub panel, plus the 60 amp breaker for the detached garage, I was just looking at the wires for the 20 Amp circuits and it appears that they might be long enough to re-route to the new sub panel but if they weren't I believe it's ok to extend them with 12AWG wire and wire nuts within the main panel .
Since it's only a total of 5 circuits in the sub panel, could I get away with no disconnect breaker in the sub panel ? I suppose it's not a big deal ( just another $80 or so for the breaker to use as a switch) to put a breaker to act as a disconnect in there but If I could save that space I think it would be good.
So Summary- Main panel is full, Need to add a 60Amp feed to a detached garage sub panel, Thinking of making room in the main by adding a sub panel at the house next to the main, and moving four 20Amp circuits to it and feeding the new garage sub panel with 60 amps from the new sub panel at the main house. Any problems with this idea?
EDIT- and yes, I know to only use the main as the tie point for ground and Neutral!.
We have done the load calculations (200Amp main service) and we're ok with the additional loads of the garage- Already have the permits in hand to do the work, but hadn't counted on a completely full panel.
I have an idea- can I put in a new sub panel at the main house, and feed it with a 80 amp breaker and ( or there about's) to it, using 4AWG CU for the 2 ft between the main and sub unless it needs to be more than 80Amps. Move 4 20 amp circuits over to the new sub panel, plus the 60 amp breaker for the detached garage, I was just looking at the wires for the 20 Amp circuits and it appears that they might be long enough to re-route to the new sub panel but if they weren't I believe it's ok to extend them with 12AWG wire and wire nuts within the main panel .
Since it's only a total of 5 circuits in the sub panel, could I get away with no disconnect breaker in the sub panel ? I suppose it's not a big deal ( just another $80 or so for the breaker to use as a switch) to put a breaker to act as a disconnect in there but If I could save that space I think it would be good.
So Summary- Main panel is full, Need to add a 60Amp feed to a detached garage sub panel, Thinking of making room in the main by adding a sub panel at the house next to the main, and moving four 20Amp circuits to it and feeding the new garage sub panel with 60 amps from the new sub panel at the main house. Any problems with this idea?
EDIT- and yes, I know to only use the main as the tie point for ground and Neutral!.
Last edited: