Hi guys and gals!
I have a serious problem in my breaker box and need as much help as I can get. My wife and I went shopping just before dinner and came home to our breaker box is disarray. Half the house is dead or using minimal power.
First, Capt Obvious says check for tripped breakers. Immediately, I went for the multimeter...
So... My layout for those who need to visualize:
100a main, single switch breaker. Drops to 2 columns of 15-20a breakers.
Readings:
Left side Right side
123v 123v
74v. 74v
123v. 123v
74v. 74v
123v
It's a pattern. I went to the basement again, shortly after checking. Initially, the 74v readings were 29v. I heard the heater unit struggling, so I killed it, which boosted the voltage to 74v in every other breaker. Even the double poles are @ 123v on one and 74v on the other.
New main? New box? Wrecking ball to the house and say f#%¥ it? Any help would be great. I have a wife and kids that would really like to keep the heat going here up north. Thanks in advance!
I have a serious problem in my breaker box and need as much help as I can get. My wife and I went shopping just before dinner and came home to our breaker box is disarray. Half the house is dead or using minimal power.
First, Capt Obvious says check for tripped breakers. Immediately, I went for the multimeter...
So... My layout for those who need to visualize:
100a main, single switch breaker. Drops to 2 columns of 15-20a breakers.
Readings:
Left side Right side
123v 123v
74v. 74v
123v. 123v
74v. 74v
123v
It's a pattern. I went to the basement again, shortly after checking. Initially, the 74v readings were 29v. I heard the heater unit struggling, so I killed it, which boosted the voltage to 74v in every other breaker. Even the double poles are @ 123v on one and 74v on the other.
New main? New box? Wrecking ball to the house and say f#%¥ it? Any help would be great. I have a wife and kids that would really like to keep the heat going here up north. Thanks in advance!