Need some electricians advice

rinker1

Well-known member
Joined
Aug 30, 2008
Messages
289
Location
Ohio
I have three outdoor lights on the unattached garage and I want to be able to turn them off and on from either the house or garage. I have a conduit between the house and garage and I know it will take 3 way switches, the lights on this ckt are wired with #14. It's about 80 feet between house and garage, I was wondering if 14-3 is ok to use or do I need 12-3. Also since it will be in conduit can I use indoor wire or will it need outdoor. Thanks!
 
To avoid these ads, REGISTER NOW!

Grumpy365

Well-known member
Joined
Jan 21, 2010
Messages
623
Location
Brazoria County Texas
Is the breaker controlling the lights a 15 amp or a 20 amp?

It has been common in the past for people to use # 14 for a "switch leg" on a 20 amp circuit. While i have seen this a lot it's wrong.
 
To avoid these ads, REGISTER NOW!
OP
R

rinker1

Well-known member
Joined
Aug 30, 2008
Messages
289
Location
Ohio
Is the breaker controlling the lights a 15 amp or a 20 amp?

It has been common in the past for people to use # 14 for a "switch leg" on a 20 amp circuit. While i have seen this a lot it's wrong.

It's a 15 amp ckt
 

keweenawbee

Well-known member
Joined
Jan 4, 2011
Messages
76
Location
MN,MI
This is the perfect X-10 or Insteon application, no switch legs required, a no brainer. I am controlling everything over 2 1/2 acres with the technology.
 