Need some help figuring out sub panel

Rugerjrs

New member
Joined
Apr 29, 2021
Messages
2
Location
Stillwater, OK
So I'm trying to wire up 240 in garage and when I hook everything up I'm only getting 120 so I check the bus bars and only one is hot. The white wire coming in to bus bar on left is 0 volts and the black one going to other bus is 120. Shouldn't they both be 120?
 

Attachments

  • IMG_20210413_163227.jpg
    IMG_20210413_163227.jpg
    102.3 KB · Views: 219
  • IMG_20210413_163218.jpg
    IMG_20210413_163218.jpg
    112.7 KB · Views: 210
  • IMG_20210413_163229.jpg
    IMG_20210413_163229.jpg
    88.6 KB · Views: 194
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
wow thats a mess.

What do you get when you meter from the left lug to the right lug? you dont need to know what the line to neutral/ground voltage is if you want 240v.

Does the white wire come from the same cable jacket as the black wire on the right?
 
OP
R

Rugerjrs

New member
Joined
Apr 29, 2021
Messages
2
Location
Stillwater, OK
Yes white wire is coming from same as black one that's getting 120. So I guess my issue is somewhere before it gets to this panel?
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,007
I dont think they ran 2 hots in there. it looks like they split the line with the bottom middle red wire nut to the 2 lugs.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Yes white wire is coming from same as black one that's getting 120. So I guess my issue is somewhere before it gets to this panel?

yeah you need to go to the feeding panel and see how its hooked up. my guess is they ran 120v to this panel...but didnt know what they were doing and connected the neutral to the ungrounded conductor lug

this whole panel needs to be gutted and rewired...
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,314
Location
New Jersey
I don't think I'd replace the panel if it meets your needs. It looks like its still the latest generation of QO panel so you can get breakers.

I would however rip out the feed and re do it instead of salvaging anything. Who knows what they did there and I' not want to spend much time figuring it out.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Tear it out and start over, not even sure the panel is salvageable but the breakers certainly are not.
 

cpbrown101

Member
Joined
Feb 27, 2021
Messages
16
Location
Texas, USA
LOL it is a 120 volt panel... only 1 hot feed and one neutral/ground feed. It will only be a 120 volt panel with 1 hot bus bar. if you wanted 220 you would have to run a new feed and a new panel.
 