R_einan
Well-known member
Decided on electric heat for the shop to keep it above freezing this winter. Went with a King 7500w heater. Specs say 32A on this unit. Wired it in with 8/2 NM-B to a properly sized breaker. Shop runs on a 60a sub panel off the house run with 6awg THFN in conduit. Tried to set up a Aube rc840t-240 to run a remote 24v thermostat, but didn't get boo out of the heater. Removed the relay and required the internal thermostat. When I went to turn the heater on, the whole shop went down. Tripped the heater breaker, main subpanel breaker, and the breaker in the house as well. Not really sure where to go from here, because I have never had a power issue of this degree. Thoughts?