Context: I just installed a new permanent service pole beside the old one since the old one is about to snap off from rot. I upgraded from a 60 amp service to a 200 amp service. I have a mobile home and a shop, each with it's own service panel, and with existing wiring running to the mobile home. There is an existing 1 1/4" conduit to the shop. All wiring is copper. I am not concerned about meeting inspection but I am concerned about it being safe. At one time I knew all this like the back of my hand but after frying too many brain cells (illness) I am a bit hazy on grounding / neutral / bonding issues.
1. The wiring to the mobile home is (2) #6 wires with a #10 bare wire. The conduit to the mobile home is 1" PVC and I don't know if it goes the whole way. (Eventually the wiring to the mobile home will be upgraded. Probably when it gets moved out and I build a 16x52 portable cabin in its place.)
2. The wiring to the shop will be (3) #4 wires. (I have the wiring.) The conduit to the shop is 1 1/4" PVC. The shop has a 100 amp service panel.
3. I have 3 ground rods on hand. The mobile home panel has no ground rod. The panel at the pole only had a #12 wire running into the ground 4' for the ground. I put one of my ground rods in at the new pole and connected it to the new service panel on the pole.
4. To be clear, each building has its own service panel. The panel at the pole is basically a disconnect. I am not feeding any sub-panels off of it. Only 2 service panels.
5. There will be one 20 amp circuit at the pole service panel. It will feed a GFCI outlet right on the pole.
My Questions:
1. Can I avoid the fourth wire to the shop if I put a ground rod in at the shop, tie the ground rod to the grounds of the shop wiring at the ground bar, and tie the third leg to the neutrals of the shop wiring at the neutral bar?
2. Do I need to bond the neutral bar to the ground bar at the shop service panel? (It is my understanding that I do.)
3. What do I do with the mobile home? Can I put a ground rod in there and tie it to the grounds in the service panel?
4. Do I need to bond the neutral bar to the ground bar at the mobile home service panel? (It is my understanding that I do.)
5. Do I need to bond the neutral bar to the ground bar at the pole home service panel?
Thanks for your assistance.
1. The wiring to the mobile home is (2) #6 wires with a #10 bare wire. The conduit to the mobile home is 1" PVC and I don't know if it goes the whole way. (Eventually the wiring to the mobile home will be upgraded. Probably when it gets moved out and I build a 16x52 portable cabin in its place.)
2. The wiring to the shop will be (3) #4 wires. (I have the wiring.) The conduit to the shop is 1 1/4" PVC. The shop has a 100 amp service panel.
3. I have 3 ground rods on hand. The mobile home panel has no ground rod. The panel at the pole only had a #12 wire running into the ground 4' for the ground. I put one of my ground rods in at the new pole and connected it to the new service panel on the pole.
4. To be clear, each building has its own service panel. The panel at the pole is basically a disconnect. I am not feeding any sub-panels off of it. Only 2 service panels.
5. There will be one 20 amp circuit at the pole service panel. It will feed a GFCI outlet right on the pole.
My Questions:
1. Can I avoid the fourth wire to the shop if I put a ground rod in at the shop, tie the ground rod to the grounds of the shop wiring at the ground bar, and tie the third leg to the neutrals of the shop wiring at the neutral bar?
2. Do I need to bond the neutral bar to the ground bar at the shop service panel? (It is my understanding that I do.)
3. What do I do with the mobile home? Can I put a ground rod in there and tie it to the grounds in the service panel?
4. Do I need to bond the neutral bar to the ground bar at the mobile home service panel? (It is my understanding that I do.)
5. Do I need to bond the neutral bar to the ground bar at the pole home service panel?
Thanks for your assistance.