Need some sub panel advice

72Corvette

Member
Joined
Nov 24, 2013
Messages
13
Location
Douglasville, GA
Good morning all,

If this is covered elsewhere I apologize but I have a few questions regarding wiring in a subpanel for the basement wood shop. Any help would be appreciated. I helped my dad who was an electrician but over the last 45 years things have become a bit fuzzy. Here are my questions:
• Service to the house is 200 amp. To serve the wood shop, glass shop and the balance of the basement I was thinking in terms of a 125 amp sub panel. Does this subpanel need a main breaker since it will be fed from the existing house panel (about 2 feet from the existing panel)?
I would prefer a main but is there any issue with two breakers in series.
• The woodshop will be a one man operation so highly unlikely any two machines will be running at the same time. In this scenario is there any issues combining multiple machines on a single circuit. All of my machines require a 15 amp circuit. How many outlets can be connected to one circuit?
Thanks for any advice,

Glen
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You don't need a 125A panel, it will work, just not needed. You do not need a main, it wont hurt it, just not needed. A 100A panel, a number 6 cable and a 60A breaker makes an ideal feed. They make an 8 space panel just for this. You can connect the panels with pipe too and use different wire but the 6 cable is super easy. Your machines require a minimum of 15A, they really should be connected to 20.
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Agree with above.

A main is fine, no issues with having one or not having one.

I don't think there is a specified limit on number of receptacles. You can have as many 15A receptacles on a 20A circuit as you want, within reason. Will you be wiring with EMT/conduit? In a shop I like 4" boxes with a double duplex in each. The run two circuits to each, so each box allows you to plug into a different circuit if needed. So maybe do two walls with one such 'double circuit' and the other two walls with another.

Can do the same with Romex of course.
 
To avoid these ads, REGISTER NOW!

gungatim

Well-known member
Joined
Jan 8, 2013
Messages
8,101
Location
west mich
is the woodshop a separate building or in your basement?

if in the basement, unless your main panel is full, I see no need for a subpanel. my shop has no subpanel, in the basement, 200a main service. I have 3-220v receptacles, one for the table saw, one for the dust collector, and a third (on the same line as the table saw) for the jointer.

everything else is on 20 amp circuit. 1-man shop, I can run lights, one machine, and dust collector at any given time. I consider it unsafe to leave a machine running and go to another, so max amp draw at any given time is less than 30 amps ...

just food for thought.
 