Hello all,
I went to help a friend install a 50amp 230v breaker and outlet for a welder he bought. The 100amp subpanel is in a detached garage and is connected to the house by buried conduit. Installing the welder outlet, I ran 8awg wire through 3/4" conduit back to the panel...very short run, only a few feet. So we kill the power to the subpanel from the main breaker and I install the 50amp breaker and tie the two hot lines to it. I then look to hook up the ground wire to th ground terminal bus. This is where I am confused. In his subpanel, the neutral from the main panel is connected to a neutral bus. However, the electrician who originally connected it did not tie any of the 110v circuits to this bus. The neutrals are connected to a bus on the other side of the subpanel along with the ground wire from the main panel. Seems to me the ground and neutral busses are tied together. Isn't that a no-no? I thought I'd have to tie the ground wire from the welder outlet to the ground bus but it seems to be tied to neutral too. Is this dangerous? Metering the hot subpanel lines and each of the ground/neutral buses yields 115v. I tied the ground from the welder circuit to the bus. Now metering the welder receptacle yields 115 from each side and 230 across both hots.
Pic of subpanel showing my breaker wiring as well as where I installed the ground on the left from the welder receptacle...
Pic of main panel showing where the main neutral coming in from the utility as well as the neutral going to the garage subpanel ties in on the right side. Utility neutral is on top of right bus and the subpanel neutral curves around and ties into the bottom of the right neutral bus...
I apologize for the long post, I'm trying to be thorough with my explanation as well as questions.
By he way, it seems that everything is working fine. We ran the welder and it worked just fine. I did however have him kill that breaker after we tested it just until we are sure what we did was safe and correct. Maybe I could have left the ground wire from the receptacle out since it is connected via conduit all the way to the main box?
I went to help a friend install a 50amp 230v breaker and outlet for a welder he bought. The 100amp subpanel is in a detached garage and is connected to the house by buried conduit. Installing the welder outlet, I ran 8awg wire through 3/4" conduit back to the panel...very short run, only a few feet. So we kill the power to the subpanel from the main breaker and I install the 50amp breaker and tie the two hot lines to it. I then look to hook up the ground wire to th ground terminal bus. This is where I am confused. In his subpanel, the neutral from the main panel is connected to a neutral bus. However, the electrician who originally connected it did not tie any of the 110v circuits to this bus. The neutrals are connected to a bus on the other side of the subpanel along with the ground wire from the main panel. Seems to me the ground and neutral busses are tied together. Isn't that a no-no? I thought I'd have to tie the ground wire from the welder outlet to the ground bus but it seems to be tied to neutral too. Is this dangerous? Metering the hot subpanel lines and each of the ground/neutral buses yields 115v. I tied the ground from the welder circuit to the bus. Now metering the welder receptacle yields 115 from each side and 230 across both hots.
Pic of subpanel showing my breaker wiring as well as where I installed the ground on the left from the welder receptacle...
Pic of main panel showing where the main neutral coming in from the utility as well as the neutral going to the garage subpanel ties in on the right side. Utility neutral is on top of right bus and the subpanel neutral curves around and ties into the bottom of the right neutral bus...
I apologize for the long post, I'm trying to be thorough with my explanation as well as questions.
By he way, it seems that everything is working fine. We ran the welder and it worked just fine. I did however have him kill that breaker after we tested it just until we are sure what we did was safe and correct. Maybe I could have left the ground wire from the receptacle out since it is connected via conduit all the way to the main box?