my "shop" is in my basement. the house has a 100 amp breaker box. i want to add a subpanel for my shop, and a 240 welder outlet. i have one space open in the box, so something will have to be moved to sub panel to make room. is 8- 3 wire big enough to run to the sub panel, or do i need 6-3? what size breakers should send power to the sub panel?thank you.

Sent from my RCT6203W46 using Tapatalk
 
To avoid these ads, REGISTER NOW!

rattle_snake

Well-known member
Joined
Jun 25, 2015
Messages
5,207
Location
Chandler, AZ
What is welder current draw? Make basement sub panel rating/feeder breaker a little bigger, then select wire size based on over current device.

Example, if welder is 40A, get a >50A panel (or even a 100A if you need more breaker positions) and a 50A breaker (in house panel) with #6 wire.

#8 wire would only support a 40A breaker/feeder service.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,179
Location
SE MI
so something will have to be moved to sub panel to make room.
Who is the manufacturer of your main panel and what is the model number ?

Much easier to replace 2 existing breakers with a tandem.

If it is old and finding breakers is get difficult, you may want to swap in a 125-150A panel with more slots.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Too little information . . . .
. . . .
a) Distance from main panel to subpanel ??
b) Expected total loads EVER in the basement shop (Do it Once, Do it Right) ??
c) Pictures of your main panel (cover on . . . AND . . . cover off)

GJ Sparky's will give you all the details with enough information.
 
OP
C

cousin eddie

Well-known member
Joined
Mar 19, 2013
Messages
45
Location
western pa
i apologize for not including enough info, thru research ive learned alot since i made that post. the box is a murray lc120df. the idea of a tandem breaker sounds like a winner to me, or maybe replacing the double breaker for the dryer to run a sub panel, then running the dryer from the sub. about distance from main to sub?- well, its 25 feet from the main to the new receptical. would it be better to have sub beside main with 25' of cable to recepticle, or have 25' coming from the main to the sub close to receptacle? thank you for all the replies.

Sent from my RCT6203W46 using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
my "shop" is in my basement. the house has a 100 amp breaker box. i want to add a subpanel for my shop, and a 240 welder outlet. i have one space open in the box, so something will have to be moved to sub panel to make room. is 8- 3 wire big enough to run to the sub panel, or do i need 6-3? what size breakers should send power to the sub panel?thank you.

Sent from my RCT6203W46 using Tapatalk

What else do u plan on running on this subpanel concurrently with the welder? Air compressor, AC, etc???

What is welder current draw? Make basement sub panel rating/feeder breaker a little bigger, then select wire size based on over current device.

Example, if welder is 40A, get a >50A panel (or even a 100A if you need more breaker positions) and a 50A breaker (in house panel) with #6 wire.

#8 wire would only support a 40A breaker/feeder service.


Depends on the type of wire... NM-b yes. THHN no.

You need to up size your main panel. The 100 amp panel isn't enough to supply the house and a sub panel.

How can u make that determination without knowing all the loads in the house? U have NO information to go on...
 